Lucien here is the article without the diagrams ..... I understand what you are saying and take on board your expertise and hands on experience and maybe you could have a look at the copy and pasted info. I am a newbie so am in the hands of those in the know and a little bit of knowledge can be dangerous which is why I am grateful to people like you yourself for taking the time and trouble to assist me !

The type of test applied when PAT testing an
appliance essentially depends of the electrical
classification the appliance falls into. However, it
is not always as simple as some believe it to be.
Here we look at two Class 1 products a kettle and
a modern electronically controlled washing
machine. Kettles have changed little over the
years but automatic washing machines along
with other major white goods have internally
changed quite a lot. Therefore depth of
knowledge and practical experience of the
product being tested becomes extremely
important as this rather simple explanation hopes
to illustrate.
L
E
N
The schematic diagram on the left is of the
electrical circuit of a standard kettle and it shows
the operating circuit the appliance mains lead
connects to. The following is only considering the
‘Insulation Resistance’ test of the PAT test
procedure in order to illustrate the need for
knowledge and practical experience of product
when testing appliances.
When a Class 1 appliance is correctly connected
to a PAT tester for the insulation test i.e. plugged
into the three pin supply on the PAT test unit and the earth test lead connected to a suitable earth point on the
appliance the test can begin (in this instance it would also require enough water added to the kettle to cover the
element (as a dry element could give a false reading).
When the PAT tester applies the required insulation DC test voltage (for a 230 AC volt appliance this will be 500
volts DC) they will (should) ensure that the On/Off switch of the appliance is in the On position so as to ensure
that the test voltage reaches the internal components that are after the On/Off switch. In this instance the
heating element.
Interestingly it can be seen in this instance that the appliance only has a single switch on the ‘live’ supply to the
circuit the therefore a test reading could still be obtained even if the On/Off switch was not closed . Although this
would not constitute a professional approach to testing such products.
A basic view of PAT testing Class 1 appliances - Part 2
The schematic diagram below is another Class 1 appliance in this instance a modern ‘computer controlled’ washing
machine. Unlike the kettle this appliance has far more internal components and more importantly has a more
complex wiring system. As before the three core mains lead connects to the appliance and in this instance passes
through a suppression unit before continuing on to the main control circuitry (PCB). If you look closely as the top of
the board the L & N terminals connect to two ‘Normally Open’ relay switches i.e. they do not ‘latch’ mechanically
as with simple push On and push again for Off type mains switches. These PCB mounted ‘relay switches’ can only
close when instructed to do so i.e. when a programme has been selected and the ‘start’ ‘short stoke’ low voltage
selection button is pressed. NOTE: This action ’Cannot’ be carried out when using the PAT tester for insulation
testing. Therefore an insulation test on this type of circuitry is unable to go beyond the two ‘Normally Open’ relay
switches which means that critical components such as the heating element, wash motor etc. are not tested. In
such cases the applied test essentially only tests the plug, the mains lead, the suppression unit and the two wire up
to the main control board. Although there are methods of compensating for this type of situation it takes
knowledge of the product and additional equipment as a PAT test unit is unsuitable for the additional testing
required.
 A point to note is that there are many other appliances that utilise ‘double pole’ switching.
 Are you or your supplier of product aware of these features?
 More importantly is the person charged with PAT testing the appliances?
Normally ‘Open’ relay switches are found on many products - washing machines, washer dryers, dishwashers ,
microwave ovens etc. in-depth appliance technical and practical knowledge is therefore required when testing such
products.
A basic view of PAT testing Class 1 appliances - Part 3
Why are there concerns with using a PAT test to verify that reconditioned/refurbished major appliance and
what are they?
 Firstly PAT testing procedures were not primarily designed for the specific purpose of verifying electrical safety
of reconditioned/refurbished appliances. The PAT testing procedures, guidance and resulting ‘none
mandatory’ ‘qualification’ target was for electrical appliances used in the work place.
 Instead of developing a testing procedure specifically for the reconditioned/refurbished sector it was deemed
by the powers that be that the PAT test procedure should implemented so as to indicate a reconditioned/
refurbished appliance was electrically fit for resale.
 PAT testing requires an operative only to be ‘competent’ in the PAT testing procedures. This can be self taught
by studying the IET guidance procedures or attending a training seminar where upon a ‘recognised’ certificate
of qualification (2377) is issued. Unfortunately such courses are often of one days duration regardless of any
pre-existing knowledge or not and an open book written assessment is often carried out to verify ability. This is
an area of concern in itself as the simple ability to follow guidance procedures is not a demonstration of the
individuals depth of technical knowledge and practical understanding of the various types of equipment
needed to safely and effectively carry out such testing and just as importantly know when testing should not
be carried out.
 Many in the Recycling sector choose to employ/use ‘qualified electricians’ that have gained the above
certification/qualification. However, although electricians will have had to demonstrate extensive technical
knowledge, understanding and practical experience of electrical installations such knowledge rarely if ever
covers the internal workings of electrical appliances themselves. As can be seen from the two simple scenario's
on pages 1 & 2 appliance construction and function are a key factor in ensuring that safety testing is not just
skin deep.
What would be the result of simply applying the PAT routine to the scenario on page 2 i.e. an appliance with
double pole latching relays?
As stated the applied PAT ‘insulation’ test would essentially only test wiring and components up to the two ‘open
circuit’ relays and if there were no problems up to that point then the appliance would be labelled ‘Passed’.
However, as can be seen the items beyond the two latching relays would not have been subjected to the
‘insulation’ test which an EEESafe DAT or DAR is required to undertake.
What could result if the above occurred?
Firstly lets assume that the components beyond the latching relays were unknowingly OK i.e. above the required
minimum insulation level then essentially there would be no problem with labelling the item as passing the
applied safety test. However, this scenario is reliant on luck and not fact. In reality there are many reasons that
wiring and/or component within appliances may have degradation (a breaking down) of their insulation. In
relation to the washing machine scenario on page 2 the two most likely items for lower than acceptable insulation
are the heating element and main motor and these are also common items across a range of such major
appliances.
What could be the result of having low insulation of items not tested?
Like all accidents and incidents things are rarely all that simple and the result if any bad or good are more often
than not dependant on a series of apparent diverse factors coming together. In this scenario if the appliance was
passed as ‘Safe’ and was correctly installed into a premises which had the correct electrical supply criteria
depending on the severity of the insulation breakdown the appliance may work for sometime before failing by
blowing a fuse or tripping and RCD (Residual Current Device ) or similar protective device. Annoying for the
customers and not instilling confidence in the suppliers of the supplied product either.
However, the installation of appliances is in itself often not carried out to a suitable standard (as essentially none
exists). In the case of washing machines (and similar appliances) it is often a case of - connect fill and drain hoses -
plug it in - fill and empty the appliance and leave. In many instance it does not even go that far. All Qualifed
EEESafe DARq’s who undertake delivery, will be required to record the required safety readings.
A basic view of PAT testing Class 1 appliances - Part 3 continued
What’s the problem with that it works doesn’t it?
The problem is that just because something works it does not mean it is doing so correctly or more
importantly ‘Safely’. For instance if the installation of the premises had a poor or none existent earth in
the electrical supply then components with ‘low insulation’ could essentially make the external metal
shell of the appliance ‘live’ to the touch exposing those in the vicinity to electric shock hazard or worse
electrocution. However, there is another potentially fatal event of greater magnitude that could occur
in such instances and that is fire.
If an installation has a poor or none existent earth in the supply the appliance would be unable to
rupture (blow) its protective fuse which could result in a faulty component over heating and in a worse
case scenario setting fire to the appliance and its surroundings.
*There are numerous variables that can adversely or otherwise affect the outcome of the safety issues
raised which have not been included in an attempt to keep the article understandable by those not so
technically knowledgeable.
 
I've only read this for gist but it would help to see the dwgs. Does it actually show the schematic of a genuine real-world washing machine or appliance with double-pole control relays, or is this only a theoretical example?

I'm wary of the number of slips and simplifications in this text, that suggest it is less than authoritative. Odd terminology, a couple of unwarranted assumptions...
 
Hi here is the link to the material .pdf format it's file in the google cache so you need to copy and paste the search data too ----> <---- copy and paste everything between the arrows and then hit return sorry if this sounds like me teaching you to suck eggs . you should then be offered the opportunity to download the original pdf document. If you use linux like me it just downloads and opens without any fuss or bother if you have android mac ios or windows then you might need to download something to open said doc. to be honest given your electrical knowledge and abilities it's likely that you are already well aware of this procedure. it may even open direcly in your browser by simply clicking the link.

---->http://www.google.co.uk/url?sa=t&rc...n5TP1oIvBfJh293vItWXTQA&bvm=bv.79142246,d.d2s <-----------
 
So the guy writing the article has probably misread the drawing. I read 'Mains contacts within 16-way programme selector switch'. I.e. not a relay, a user-operated switch, that presumably DP isolates the machine when no programme is selected. You will see that all the internal programmer controls, whether triac or relay, are single-pole only. In this case many of them are in the neutral but the test voltage will reach the loads so long as a programme is selected.

What he could have picked up on, that illustrates the point perfectly, is that the heating element is controlled in both line (programmer relay) and neutral (pressure switch). Therefore the element is not under test until the machine is filled to normal level with water.
 
I'm beginning to get the idea Lucien

"What he could have picked up on, that illustrates the point perfectly, is that the heating element is controlled in both line (programmer relay) and neutral (pressure switch). Therefore the element is not under test until the machine is filled to normal level with water. "

That bit of data has been written to memory.
 
How many phase is your Mercury Arc Rectifier by the way Lucien and what type of equipment would you need to give it a PAT test I wonder ? I gather there was a working example on the Blackpool tramway until quite recently !
 

Reply to Pat testing help in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
750
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

what is the piece of equipment and part number?
Replies
9
Views
720
out of interest UK, how do you know what kit is connected?
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top