Have things changed and I missed the memo.
Let's start by saying I'm a fossil. I was trained the old way, were u went with a mate and went to night school and day release. Anyway, was on a domestic fault for a mate of a mate. I rocked up, kitchen ring tripping. Asked any recent works, holes drilled etc, non was the reply ( which was a fib, but no matter). Took both legs out of the board, circuit breaker tests ok, ring has 48k short. Went to split the ring mid point and noticed no earth strap from the box to the socket ( in my day this was mandatory). Found fault, someone had fitted an outside socket, full of water. Anyway back to the internal metal back box. The ring was in a new extension, one year old. So I advised them to get the sparks back to fix it. A few days later, customer rang me and said the sparks said it's not a requirement anymore. My question..since when
 
Usually, if one of the screw lugs are fixed it is deemed that the metal k.o box is earthed through the 3.5mm screw and eyelet of the socket or other accessories if the designer/installer feels that this mechanical contact is poor or future deterioration is likely then an earth flylead is
required. If both the lugs are adjustable then this is classed as unreliable. There is nothing wrong with going beyond the minimum standard set down by BS7671.
 
I don't do it on plastic I started in 2006 so guess we were on 16th and no longer a requirement then. I know from doing periodics thinking back the one fixed lug making contact with the brass ring round the screw hole was deemed sufficient, was brought up on site work so wouldn't often do more than required in that situation and old habits die hard whichever side you fall.
 
Not required. Back box is earthed by face plate screws. Could be argued you shouldn't be working live hence you shouldnt be opening it without killing power anyway
 
It’s niether extraneous or exposed
May sound bizarre on first reading, but the metal backboxes is indeed an exposed conductive part.
This is because it is not insulating and may become live under fault conditions.
The touchable criteria could be indirectly, for example installed into a metal framed wall with a shelf fixed on the other side. Regardless, There is no requirement for any specific standard of insulation to the wall that encloses the back box and the back box is the only thing under the control of the electrical installation.

Having said all that, the screw is deemed enough to earth it!
 
Agreed on both point. But A) why have the termination screw o the box if it's not mandatory and B) why was I told to do it and have always done it since I was a lad?
Somewhere to hang your cpcs if the wiring is Twin and cpc, on a lighting switch maybe, where there is no earth connection on the switch?
 
Seems just like a nice finishing touch, takes less than a minute, and on surface-mounted metal-clad stuff in a workshop with multiple users of varying skills it makes sense as an extra safety element, imho
 
Also helps to use up that roll of 1.5mm green/yellow 6491 that will not ever end.
As with @Murdoch - any upgrades to metal switch faceplates is a must.
The termination block is there for when a switch is to be fitted, stops a floating earth
You bin watching Sy Fy movies Mate floating earth WTFs that all about.
 

Reply to PE from metal back box to socket in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
657
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top