Have things changed and I missed the memo.
Let's start by saying I'm a fossil. I was trained the old way, were u went with a mate and went to night school and day release. Anyway, was on a domestic fault for a mate of a mate. I rocked up, kitchen ring tripping. Asked any recent works, holes drilled etc, non was the reply ( which was a fib, but no matter). Took both legs out of the board, circuit breaker tests ok, ring has 48k short. Went to split the ring mid point and noticed no earth strap from the box to the socket ( in my day this was mandatory). Found fault, someone had fitted an outside socket, full of water. Anyway back to the internal metal back box. The ring was in a new extension, one year old. So I advised them to get the sparks back to fix it. A few days later, customer rang me and said the sparks said it's not a requirement anymore. My question..since when
 
Why are folks getting so excited about adding the flylead if its a metal accessory?
I can kind of understand if you mean when replacing a plastic light switch for metal, and cpcs were already terminated in back box, easier just to add fly lead, but in every other instance I'd always prefer to run cpcs direct to accessory, and leave it at that.
For some reason on metalclad surface mount gear I always fit a flylead, but tend not to bother with flushboxes. Beginning to question the logic with that but there you go!
 

Reply to PE from metal back box to socket in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
677
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top