Can anyone please shed some light on what this is/what is going on here?

This old apartment is wired in conduit, which is also the earth provision. In the bathroom, this metal 'thing' is screwed into the side of the pendant backbox. Out comes a fly-lead also connected to the pendant backbox, and in goes a neutral from the light, as does another leading off in another direction.

If I disconnect the neutrals and stick them into a wago the light fails to work. I found it just as the day was wrapping up, so I haven't fully investigated, but I'm assuming they're using the conduit to provide a neutral? If so, then why is the RCD not tripping and what is this odd contraption?



Screenshot 2023-03-01 at 18.18.37.png
 
Ahhh ffs, I think you are right. Well, this job is about to get interesting. The reason the light came down in the first place is because the LED was flickering whilst the switch was off, suggesting some leakage going on. Now I've got this in the mix.
 
That MI seal is poking into the BESA box instead of being seated inside the gland screwed into its conduit entry. Advantage; you can see and get to the seal, offset against it hogging the space inside the box. The MI sheath is the earth but shouldn't be serving as the neutral; that practice was used historically (earthed concentric wiring) but not in domestic work. If someone has picked it up as a neutral he's a very naughty boy.

There should be two or three sleeved conductors exiting the black disc in the end of the pot. Some later seals also have an earth tail spot welded onto the pot itself which is securely in contact with the MI sheath, but more commonly the earth connects only via the gland (which you can't see) and box as a conduit would. Try to avoid flexing the conductors too close to where they exit the pot because if they break off, or the disc comes loose, you have a more complex job on your hands.

A failed or damaged seal allows the MI insulation to absorb moisture from the air and its insulation falls. If one end or the other has got very bad or there's a puncture in the cable sheath somewhere, it might have fallen low enough on a switch cable to cause flashes when off. Although, if the MI doesn't contain both the PL and SL conductors, that's not the problem here. If it's suspect, disconnect all cores and megger to the sheath.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Pendant backbox - what's going on?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
JosephandAmber,
Last reply from
Lucien Nunes,
Replies
5
Views
1,341

Advert

Back
Top