AS an apprentice yes isnt that i would be looking for after this course.
I dont see myself as an experienced electrician and would be foolish to after doing a fast track course however it gives me the paperwork i need to be able to apply for mcs,which i believe you need to be part p reg for ,2 years ago it never crossed my mind to be an electrician but had so many customers asking about solar installs that i thought it would be sensible to offer the service myself,since then i have been on a few installs with our sparkie to gain experience whilst doing the course,i can understand some of your opinions but whats wrong with improving yourself and your business.
I'd be interested to know where you stand on bonding or is it earthing, perhaps you could tell us, a frame if it's a TL inverter and the system is a PME
Do you know why if you do use a TL inverter, that if a RCD is required why you need a B type
I'd also be interested in knowing what you think about bonding or is it earthing a frame that does incorporate an inverter that as a transformer, but can be reached through a dormer window.
What is your take on RCD protection when a manufacturer insists on 100mA RCD for the inverter but you have to supply the circuit with additional protection as in the regs and fit a 30mA one
What is your take on If RCD protection is required, how would you sit when a fault occurs on the circuit and the RCD must trip within 40mS, but of course the inverter will not shut down in that time,do you have proposals or scenarios to over come this.