K&L_Electriccal

We did a 5 yearly periodic inspection report on a care home a few week ago that was built in “august 2005” the only RCD protected circuits we found was for the out side sockets, none of the sockets inside had any so what would you guys recommended for this if any,

Cheers lee
 
I would think it is a 4, however, you should code any socket that can "reasonably" be used for outside appliances as a 2 which are not RCD protected.
 
Don't we just love the codes no RCD protection for sockets well in the ESC guide it states it should be a 2 and gives an example of sockets in a TT system. In the OSG example it also gives it a 2 for just sockets in general.

Personally I also think it should be a 2 requires improvement. Did you find any of the bathrooms or shower rooms with RCD protection? and if they didn't have it, and needed it, what did you code them?
 
ESC guide states a 4 for a socket that is unlikely to supply equipment outdoors and is not in a bath or shower. The op stated that outdoor sockets have RCD protection.
 
It a code 1 lol thought id throw that one in did an inspection on friday , flat screen TV on the side of the bath plugged into an extension lead which was in a socket that wasnt RCD protected .... and guess what i had no camera with me why does it always happen no normally a code 4
 

Reply to periodic inspection report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
708
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top