Periodic inspection | on ElectriciansForums
Discuss Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
London
Hi am doing my first periodic inspection for a restaurant, my understanding is that I need to test a percentage of installation, so can I test some circuits and leave others? And if I could perform a certain test on a circuit how can I fill the schedule of results? Thanks
Depending on the age and condition of the installation, it could be 100% of circuits need to be tested.
Paperwork from previous tests is a good place to start if they are available
The installation to be honest looks in a good condition, the problem is I could find any paper work from previous tests, and some circuits I can't power them off to do all tests, and now am confused how to fill the schedule of test results
percentage testing means testing a percentage of points on each circuit, but all circuits need to be tested. it does not allow for any circuits to not be tested at all.
I thought all circuits initially need fully testing no excuses
Then once you have done this you can agree to test a certain percentage of circuits at regular intervals
You can "not test" a circuit, for instance it is quite normal not to turn off a comms supply. However, use your initiative. In a restaurant its probable that there is little you cannot test, on the certificates there is a box which says operational limitations
We did an EICR a few years ago, everyone was happy we were turning power off and on etc, Monday morning, 2 network switches had blown their power supplies, just due to power off, power on,
Too many limits though and you end up with a piece of toilet paper.
You should have a really good reason for not powering down a circuit, just limiting circuits means you could be leaving potentially dangerous circuits in play.
Reply to Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Thanks Risteard. I had put it down as a 2, even though I wasn't sure if I was right in doing so. Good to hear you'd have done the same. Thanks for...