Changing the fittings is a bodge solution
Of course it's a bodge, and my notes would recommend rewiring the circuit, but it's a bodge that makes the installation satisfactory. We can't make up coding to suit what we'd recommend the installation to be.
 
Thank you guys your comments have been very helpful! Just one more what are are duties and if we are carrying out an EICR and we spot a C2, I know for a C1 we’d make safe as there is a danger present but a C2 it’s only present if a fault occurs. Just trying to get my head clear for my 2391-52?
 
Thank you guys your comments have been very helpful! Just one more what are are duties and if we are carrying out an EICR and we spot a C2, I know for a C1 we’d make safe as there is a danger present but a C2 it’s only present if a fault occurs. Just trying to get my head clear for my 2391-52?
I'm not trying to be funny but out duty is to inspect and test according to the agreement with the client. If we find C1's we need to exercise judgement about whether to isolate or negotiate an instant fix (sometimes the rest of the inspection needs to be delayed to accommodate this). If we find C2's then by definition they are still one fault away from instant danger and the person receiving report has the responsibility to arrange the necessary work.
Of course we can quote for that work, and sometimes clients prefer to say "fix as you go" within reasonable constraints.
Does that help, or confuse further?!
All the best for your exam.
 

Reply to Periodic inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
626
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
781
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
924
What readings were you expecting for the cable prior to testing? What is the make of the protective device? Is there any previous paperwork [test...
Replies
3
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top