what is the correct order for a periodic test ??
is it different to the order for the initial testing for a new cct.
 
what is the correct order for a periodic test ??
is it different to the order for the initial testing for a new cct.

Periodic:
Continuity
Ring continuity
Insulation resistance
Polarity
Earth electrode resistance
Earth fault loop impedance
RCD (+ functional test)

Initial testing:
Continuity
Ring continuity
Insulation resistance
Site applied insulation
Protection by seperation of circuits
protection by barriers or enclosures provided during erection
insulation of non-conducting floors & walls
Polarity
Earth electrode resistance
earth fault loop impedance
Pfc
RCD (+ functional testing
 
Initial verifications testing -

Each circuit must be tested in order of sequence as stated in guidance note 3 ( or the above, easyfox's post)

Periodic testing,

the level of testing will depend largerly on what the inspector discovers during the visual inspection.

if any tests show significant different results, then further testing may be required

some times, up to 100% of the installation will need to be tested

there is no set sequence for the testing which may be required, its left to the competent persons carrying out the tests

Periodic Inspection

a minimum of 10% of the installation should be inspected, obviously it could increase if defects are found.


hope that helps regards luke
 
Periodic:
Continuity
Ring continuity
Insulation resistance
Polarity
Earth electrode resistance
Earth fault loop impedance
RCD (+ functional test)

Initial testing:
Continuity
Ring continuity
Insulation resistance
Site applied insulation
Protection by seperation of circuits
protection by barriers or enclosures provided during erection
insulation of non-conducting floors & walls
Polarity
Earth electrode resistance
earth fault loop impedance
Pfc
RCD (+ functional testing


Pardon? Why wouldnt you do PFC (both of them) on a Periodic? How many householders would actually hand you a copy of the EIC or the previous PIR?

And the same goes for site applied insualtion etc. Down to the inspector. And of course, if you are measuring Zs when you already have R1+R2 and Ze you are in direct contravention of the statutory EAWR's

And if we are going 17th edition, you could possibly add on X2 RCD checks, X5 checks on ALL RCD's (even those above 30mA) - like to see you all do THAT with youre Flukes! And verification of phase sequence for 3 phase, and of course verification of voltage drop using circuit impedence:eek:

if you want to REALLY have fun!:)

Cant wait for the new GN3..........
 

Reply to periodic test ????? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Check out pages 92 and 93 of GN3 for help.
Replies
18
Views
2K
I have a number of Limitations are part of my Testing work in my current role. I test as much as practicable and not down any limitations on a...
Replies
2
Views
393

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top