This is my first post on the forum so here goes! ..............................................................As it has already been said initial verification on new installations is 100% of every circuit. Periodic test and inspection is different in that it is more inspection than test. The testing scope can be influenced by the client operations and you need to get this agreed with them before you start under the limitations. You may have a situation where the client has a comms / Data room which cannot be switched off, so they may require a visual non-intrusive inspection and no testing. Flag this up on your certification. You may also have, on the day access issues to rooms etc, note these down as well under operational limitations. In most cases its what you havent done as opposed to what you have done that needs to be highlighted to the client on the paperwork. Buildings with test records I would aim to carry out a test on 20% of the final circuits, and compare readings if you find anomallies do a further 20%. I would also carry out an Insulation resistance of the whole DB Neutral to earth as a N-E fault is the most common to go undetected, you wont flag it up by doing a ELI test or even the plug in 'Martindale' tester. If you are unsure as to end user electronic equipment initially carry this out at a reduced voltage of 250V dc. Periodic testing you don't follow the same testing sequence.

If there are no test records, you need to tell the client from the outset that a full 100% test is recommended, again thay may not want you to do it, operation / cost etc so get it written down in your limitations. If they dont want it and are not going to pay for it then dont do it just cover your self on the documentation.
 

Reply to Periodic Testing Percentage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
Replies
3
Views
328
  • Question
I think the point made here on knowing the calculations for verification of results etc is a good one. With one question leading onto the next not...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top