Could anyone out there give me a detail explanation on what is the above test reading proving, is it that you have for a very low reading good continuity through the connections at the equipment at the origin of a installation. And what makes the reading vary from one installation to another.
 
prospective short circuit current is the highest current that can exist in an electrical system under short circuit conditions, it is determined by the voltage and impedance of the supply so PSCC= voltage/Ze
 
prospective short circuit current is the highest current that can exist in an electrical system under short circuit conditions, it is determined by the voltage and impedance of the supply so PSCC= voltage/Ze
Not necessarily, in a TN-C-S PEFC and PSCC will be the same (give or take) but in other earthing systems they are not going to be the same so the calculation you post isn't always going to apply.
 
As far as I remember, through a slightly drunken haze, Lee the calc you posted relates to PEFC only although I do stand to be corrected on that. As I say, I'm half cut just now.
That's why both PEFC and PSCC are measured, one of the many things the test is useful for is making sure the MCBs aren't going to explode into a million different pieces when the fault current happens, or to put it another way, that they have sufficient breaking capacity.
It also proves that you have a viable earth and that the impedance of the earth fault loop is withing specified parameters
 
is pfc measured phase to earth and pscc phase to neutral?
pEfc is measured between live, neutral and earth conductors because it is measuring the prospective earth fault current. IE that fault current that will flow between live conductor(s) and earth.
Whereas prospective short circuit current is measuring that which will flow if a short occurs between live conductors IE live and neutral.
The higher of the two readings is referred to as the Prospective Fault Current (pfc) for the installation. If you're sitting a testing exam you have to make sure you get the terminology right mate.
Make a mess of your terminology and you are going to drop points.
 
You might think I'm being needlessly pedantic Lee but I get the feeling you're a trainee so it has to be drummed in that you have to get the terminology right. This isn't like school mate, C&G examiners will not give you the mark because they know what you mean.
 
You might think I'm being needlessly pedantic Lee but I get the feeling you're a trainee so it has to be drummed in that you have to get the terminology right. This isn't like school mate, C&G examiners will not give you the mark because they know what you mean.

no not a trainee, but must admit some times my terminology isn't up to scratch so to speak, I am graded as approved on my jib card lol
 
Peeps seem so quick to forget Mr Zl.....
 
Peeps seem so quick to forget Mr Zl.....

Indeed. I will usually do a line impedance check at the same time as I do a Zs. It's a quick way of checking the integrity of the neutral path. I think it's odd that it's not used more.

OK, maybe it's not such a dangerous situation as a line to earth fault, but in the event of a line to neutral short, it's the line impedance that determines the disconnection time.
 
Indeed. I will usually do a line impedance check at the same time as I do a Zs. It's a quick way of checking the integrity of the neutral path. I think it's odd that it's not used more.

OK, maybe it's not such a dangerous situation as a line to earth fault, but in the event of a line to neutral short, it's the line impedance that determines the disconnection time.

But if the line impedance is high then it will be noticed very quickly as it will affect the normal operation of the installation.
 
It may not just be the neutral path but by poor design live and neutral, whereas a satisfactory Zs reading may be obtained by parallel paths.
I also think it a good idea to conduct a Line impedance test, particularly where Zs readings are close to their limits.
 
But if the line impedance is high then it will be noticed very quickly as it will affect the normal operation of the installation.

Indeed, although dependent on how heavily it's loaded and the type of load. If it's just a heater, poor line impedance won't be noticed as quickly as, say, lighting.
 
PFC is the generic terminology used for Prospective fault current, whether it is PEFC or PSCC.

It then breaks down as thus

PEFC. Prospective Earth Fault Current. A fault between a LIVE conductor and EARTH. A LIVE conductor can be a LINE or NEUTRAL conductor.

PSCC. Prospective Short Circuit Current. A fault between LIVE conductors. The highest current will flow in a fault between all 3 LINE conductors.

Although some test instruments can test between LIVE conductors, it is generally not acceptable as safe practice, so you would test between each LINE conductor and EARTH, and take the highest test result and double it as this errs on the side of caution, and record this value as your PFC result.

If your tester can't do a LINE to LINE test, and you try it, you may well end up with bits of plastic in your face or worse, and you wont be laughing about it in the pub, your local A&E wont think you are funny either, but the local undertaker may be thankful for your business.

Hope that clears things up a bit, and as said by someone else, the terminology is very important.

Cheers..............Howard
 

Reply to Pfc and pscc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Replies
21
Views
1K
A
  • Article
Here is Practical Explanation about Next Life, Practical Explanation ( For Example ) :- `1st of all can you tell me every single seconds detail...
Replies
0
Views
192
aptau34
A
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
  • Question
Yes I noticed that too, although the Fluke 1664 that I use claims the same precision (it has a milliohms mode in the high current loop impedance...
Replies
18
Views
3K
  • Question
Your wife is irrelevant, save that for the general forum. This is the trainee forum, if you cannot treat the trainees with respect and courtesy...
Replies
6
Views
3K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top