Nicktric

Hi I am confused with my readings for Pefc as my Ze is .09 which would give me 2.55Ka but when I test PFC on my meter I get 5.62Ka? Ze, Neutral and earth leads clipped on disconnected main earth, probe Line on Supply side?

Can I check I am doing this correctly;3 lead PEFC piggy back Neutral/Earth clip on MET test on supply side of RCD. Pscc Clip on MET earth lead probe Line and probe Neutral supply side RCD?
Thanks
 
The Ze should be measured with bonding disconnected, PFC with bonding connected to get a worst case scenario, this normally means that measured PFC is higher than V/Ze.
 
as IQ's post. parallel paths will give you a higher value when measured than you would expect from the Ze reading. out of interest, you could re measure Ze with all the bonding and earthing connected, then re calculate PFC. ( not for the records, just to prove a point )
 
HI, CAN SOMEONE HELP ME ON THE PROCESS FOR TESTING Ze,
Q: isolate the supply,disconnect the main earthing conducter (MET),put the earth lead on the disconnected earth and the neutral on the supply side,and the live and the supply side,then test, and record the value? (am using a fluke 1653b)
 
Last edited by a moderator:
HI, CAN SOMEONE HELP ME ON TESTING FOR Ze

I can hold the meter?

1 Isolate the installation

2 Remove the earthing conductor from the main earth terminal to eliminate any parallel paths

3 Test between line and earthing conductor at the live side of the main switch.

4 Record the result and reconnect the earthing conductor before energising the installation.

There are other text book answers regarding GS38 and other safety issues but the basic test is as above.
 
Have done the Ze,using fluke 1653B got two reading one for the PSC L-N 0.27ohm,901amps and PEFC L-E 0.36ohm,676amps, which of the highter value should i take,is it the ohm or the amps value.the R1+R2 reading for the light circuit is 2.35ohm,i should then add it to the highter value of PSC,PEFC and record it on the schedule of test results in column *12 (EFL Zs)

just trying to get on top of this,taking my 2391-10, on the 9-06-2011,so i need all the help i can get, thanks in advance
 
Your Ze is the test done with your main earthing conductor removed and as IQ note above you clip the disconnected earth and the LINE conductor on the supply side of your isolated switch and take the ohm reading

Your prospective earth fault current (PEFC) and your Prospective short circuit current (PSCC) is tested with the earth conductor re-connected to the MET. PEFC is done with clip to MET then to LINE and the Ka rating is taken. The PSCC test is between LINE/NEUTRAL and the Ka is taken, which ever is the highest is the value you take. Note on a TNC-S the chances are thje values will be near enough the same.

The Zs value for you lighting circuit is Zs = Ze + ( R1 + R2) so the PEFC and the PSCC should not come into the equation.
 
well what should i do then..anyone what a cup of tea?

you can explain then to me the reading that i got from doing IR,i have loads plug in that i cant plugs, so i then, from the CCU, yes isolate the supply connect the L-N togehter and test to E and i got a reading of about 22.8 m ohm, and the fluke 1653B set on the IR 250v,that was downstair,but when i do the same test upstair with eveything unplug the reading was >200.00,which is fine i think?
 

Reply to PFC Calcs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
490
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top