readings are fine. the 22.8Mohm is probably due to appliances still being plugged in.
 
If you're measuring PFC then forget Ohms, it won't be a true Ze value as bonding should still be connected.

Record the highest value as PFC.

On Ze you have to have parallel paths removed and you are measuring between line (s) and earthing conductor, highest value recorded.

Zs=Ze+(R1+R2)
 
Your Ze is the test done with your main earthing conductor removed and as IQ note above you clip the disconnected earth and the LINE conductor on the supply side of your isolated switch and take the ohm reading

Your prospective earth fault current (PEFC) and your Prospective short circuit current (PSCC) is tested with the earth conductor re-connected to the MET. PEFC is done with clip to MET then to LINE and the Ka rating is taken. The PSCC test is between LINE/NEUTRAL and the Ka is taken, which ever is the highest is the value you take. Note on a TNC-S the chances are thje values will be near enough the same.

The Zs value for you lighting circuit is Zs = Ze + ( R1 + R2) so the PEFC and the PSCC should not come into the equation.

Sorry am getting myself mixup, i did disconnect the earth, so the value i got is 0.36ohm, 676amps, so this should record in form4 *2 and *3
 
PEFC is done with clip to MET then to LINE and the Ka rating is taken. The PSCC test is between LINE/NEUTRAL and the Ka is taken, which ever is the highest is the value you take. Note on a TNC-S the chances are thje values will be near enough the same.
Hi Malcolm,
can I just check 3 probe set up PEFC join earth and neutral probes then probe MET and line supply side. Then PSCC Neutral and earth probes joined, probe Line and Neutral supply side?

Cheers
 

Reply to PFC Calcs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
490
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top