readings are fine. the 22.8Mohm is probably due to appliances still being plugged in.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss PFC Calcs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Your Ze is the test done with your main earthing conductor removed and as IQ note above you clip the disconnected earth and the LINE conductor on the supply side of your isolated switch and take the ohm reading
Your prospective earth fault current (PEFC) and your Prospective short circuit current (PSCC) is tested with the earth conductor re-connected to the MET. PEFC is done with clip to MET then to LINE and the Ka rating is taken. The PSCC test is between LINE/NEUTRAL and the Ka is taken, which ever is the highest is the value you take. Note on a TNC-S the chances are thje values will be near enough the same.
The Zs value for you lighting circuit is Zs = Ze + ( R1 + R2) so the PEFC and the PSCC should not come into the equation.
readings are fine. the 22.8Mohm is probably due to appliances still being plugged in.
So i should record this 22.8 M ohm in IR,L/E column *10, in sted of >200
Hi Malcolm,PEFC is done with clip to MET then to LINE and the Ka rating is taken. The PSCC test is between LINE/NEUTRAL and the Ka is taken, which ever is the highest is the value you take. Note on a TNC-S the chances are thje values will be near enough the same.