Alreet all,

Went for an interview for a FM company recently and got asked a couple of, what I thought were, ambiguous questions.

Thought i'd find out what everyone else thinks.

1) What would you expect to find during PFC test?

&

2)What would you expect to find during Earth Loop Imp test.

Answers on a postcard.........


Neil.
 
Possibly the following:

1) A result in kA that determines the fault current likely to flow in the event of a fault. The lower the external impedance of a supply, the greater the fault current would likely to be. I'd also explain to make a note to check whether the MCB's/RCBO's and switchgear within an installation are likely to be rated to the prospective fault current.

2) A result in ohms, which complies with the relevant earth system value, TT, TNC-S, TNS etc. The Zs result that you obtained may also need investigating if it is greater than your Ze test and your R1+R2 test results combined.

Any comments welcome!!
 
Thanks Test-Meter,

Answers,

1) No more than 16kA except in parts of London
2) Max 1 Ohm

Now call me crazy but that doesn't sound to me like the question they were asking.

I thought they were after an explaination of the relevance and not a max value.

I got No1 right but went into the details of Ze with No2.

Why can't they say what they're looking for rather than being vague... Jeez!
 
2) Max 1 Ohm

if they've ever worked on a TT system, they're dreaming, unless the rod/s were installed by eng54. LOL.
 
Thanks Test-Meter,

Answers,

1) No more than 16kA except in parts of London
2) Max 1 Ohm

Now call me crazy but that doesn't sound to me like the question they were asking.

I thought they were after an explaination of the relevance and not a max value.

I got No1 right but went into the details of Ze with No2.

Why can't they say what they're looking for rather than being vague... Jeez!

Well, 1 Ohm is the maximum for which system? Its 0.8 for TNS and 200+ For TT, this was a pretty poor question.
 
Can you see my confusion?

I was on about a range of values dependant upon blah blah blah...

and the answer I got

'Your over thinking it'

No specific system mentioned, no details whatsoever, just the question.
 
Can you see my confusion?

I was on about a range of values dependant upon blah blah blah...

and the answer I got

'Your over thinking it'

No specific system mentioned, no details whatsoever, just the question.

Thats a rubbish question probably taken straight from a city and guilds paper, they seem to be the main crap question purveyors!
 
typical suits. read a few bits and think they know it all.

my answers would have been.1. expect my 1552 to show a PFC reading. 2. expect it to show a Ze value.
 
I'm very familiar with C&G's type questioning, and even they wouldn't try some imaginary nonsense like that.

I'd have offered him some educating.


I've seen things like this before myself. I once went for an interview at a company in Leather head and the interviewee wrote down three formulas, each with a symbol missing and he asked me to find them. The answer to all three was 'I' and I think maybe I intimidated him from asking any more..

I got the job, but I wasn't interested any more.
 

Reply to PFC & Earth Loop Imp Tests. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top