hi all,
tested a board on a house today, TT system and got a PFC reading of 50 amps :confused:
does this sound right :confused:
ZE is just over 7 ohms
Did you check the line to neutral fault current as well? As that will also play a part as the PSCC, as the highest of the PEFC and PSCC is the one that goes in the PFC box...
The system in pscc measurement is not relevant as you are measuring between line and neutral, it is only pefc which is relevant to sytem earthing as it taken between line and cpc
also with pefc unlike Ze it is taken with the earthing conductor connected to include any parallel earth paths that may be present, hence in an industrial unit with a lot of structural steelwork to ground the pefc may well be higher than pscc and then is recorded as pfc on the cert
Reply to Pfc on a tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...