Hi,

If you have a TNS supply, you would have a separate earth path by way of lead pipe or split concentric etc... true?

Ok, so if you have a PME / TMC-S supply, the earth connects to the neutral at the service head, yes... true?

Ok, so just out of interest, if you had an overhead TT thats now been converted into a PME, would you expect the PFC and PSCC readings to fluctuate if you keep taking the reading?

I just changed a board yesterday on this supply, and it was overhead TT, now PME, and im getting fluctuating readings anywhere from 0.22 to 0.28, ive checked my meter and checked again etc, and its all ok, but its fluctuating.

The only reason I say this is because, i also changed a board i dont know 6 months ago, i put it down as TNC-S / PME as thats exactly what I saw, the readings between PFC and PSCC were 0.1 ohms different. The NICEIC bloke said You are wrong, its not TNC-S and marked me down.

I said ok, well what is it then? He said its TNS on split concentric cable...ok fair point I said, he said that if its PME / TNC-S the readings will be exactly the same.

Now this one I have just done, its quite clean cut, theres two lines and one neutral, its NOT TNS, its not possible, but I am getting fluctuating readings.

Can anyone with a bit more knowledge enlighten me please.

[ElectriciansForums.net] Pfc / pscc

I have connected the Earth into the left hand side as instructed by WPD as its been converted to PME and even has a sticker on it saying TNC-S / PME.
 
Dunno mate I wasn't there, if there is one cable coming into the neutral terminal and you confirmed continuity to the earth side of the cut out then thats the evidence you need to confirm it is indeed linked.
 

Reply to Pfc / pscc in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Yes, probably overthinkig, thanks.
Replies
6
Views
535

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top