Hi,

If you have a TNS supply, you would have a separate earth path by way of lead pipe or split concentric etc... true?

Ok, so if you have a PME / TMC-S supply, the earth connects to the neutral at the service head, yes... true?

Ok, so just out of interest, if you had an overhead TT thats now been converted into a PME, would you expect the PFC and PSCC readings to fluctuate if you keep taking the reading?

I just changed a board yesterday on this supply, and it was overhead TT, now PME, and im getting fluctuating readings anywhere from 0.22 to 0.28, ive checked my meter and checked again etc, and its all ok, but its fluctuating.

The only reason I say this is because, i also changed a board i dont know 6 months ago, i put it down as TNC-S / PME as thats exactly what I saw, the readings between PFC and PSCC were 0.1 ohms different. The NICEIC bloke said You are wrong, its not TNC-S and marked me down.

I said ok, well what is it then? He said its TNS on split concentric cable...ok fair point I said, he said that if its PME / TNC-S the readings will be exactly the same.

Now this one I have just done, its quite clean cut, theres two lines and one neutral, its NOT TNS, its not possible, but I am getting fluctuating readings.

Can anyone with a bit more knowledge enlighten me please.

[ElectriciansForums.net] Pfc / pscc

I have connected the Earth into the left hand side as instructed by WPD as its been converted to PME and even has a sticker on it saying TNC-S / PME.
 
I did see only two weeks ago on a board I changed, it was TNS with split concentric originally, then had a new head and a label put on it saying pme TNCS, so again I get two different readings, I call WPD and ask them and they say it's pme, I say how comes I'm getting a different reading and they were bang on the same each time so was confident it was as thought, they then looked at it and sure enough it was separate with a sticker saying otherwise.
 
No, not with the installation connected.

The installation was not connected, the main switch was open and the main earthing conductor disconnected.... It was just a ze reading which I was changing on the meter from PFC to PSCC, I know that it should be connected to take that reading which I do, but I was taking a Ze.

Everything I did was sound and tight and to the best of my knowledge it was correct, I can only put it down to a poo supply, it is in remote little hamlet in the middle of nowhere on a long run of overhead poles.
 
What meter are you using?
Why do you need to change settings for PSCC and PFC, both tests can be done on the same setting which should be the high current 2 wire loop test.
If your meter has been using 3 wire low current/anti trip test for one of the tests then you can expect the two results to be different.
 
Sorry wasnt making my self clear, Fluke 1654B, all three wires connected, but I just press a button to switch between L-N-E and L-N, maybe I had it on the non trip setting by mistake... I doubt it though as that takes ages and this was fast.
 
I have seen people say about the Fluke test lead issue before and have to buy new ones to resolve the issue, admittedly I have plugged them in before and when I zero the leads I occasionally get a strange reading, but I think its time to replace them! I would imagine this is all the problem is.
 

Reply to Pfc / pscc in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Yes, probably overthinkig, thanks.
Replies
6
Views
535

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top