Hey, why does gn3 say the pfc of a 3 phase sytem will always be higher on the pscc test than on the pefc?
Also when you have the pfc measurement how do you use it to select your protective conductor size?
 
because on 3 phase the pscc is measured between phases ( or L/N ) and pefc is to earth.

you select your protective conductor by means of the adiabatic equation ( 543.1.3 )
 
because on 3 phase the pscc is measured between phases ( or L/N ) and pefc is to earth.

hey thanks for the reply i understand that the pscc is between L-N or L-L, but why is this reading higher than that for L-E, i thought that L-E would have a better return path with a lower resistance so consequently would have a higher reading of KA to disconnect the protective device. GN3 claims pscc would be higher but doesnt explain why?
 
lower resistance of line conductors compared to protective conductor. L-L is < L-E.
 
If your instrument is unable to measure the PSCC between phases on a 3P system, as per single phase you measure between L&N.

The PSCC will always be higher between the phases of a 3P system than between L&N because the voltage between them is higher 400 v 230.

The actual sum is to multiply a L-N reading by 1.732 to obtain the theoretical maximum PFC between phases, however we are told to multiply by 2 to err on the side of safety.
 
If your instrument is unable to measure the PSCC between phases on a 3P system, as per single phase you measure between L&N.

The PSCC will always be higher between the phases of a 3P system than between L&N because the voltage between them is higher 400 v 230.

The actual sum is to multiply a L-N reading by 1.732 to obtain the theoretical maximum PFC between phases, however we are told to multiply by 2 to err on the side of safety.

that is spot on, thanks for the answer, makes sense now double the voltage the rest of the figures will be larger as per ohms law. sometimes its obvious when you know the answer.
 
nothing passes you spinlondon... you should be cop aka polis aka pealer, you miss nothing even better you should be a snifferdog;)

tell me this some motors dont require a neutral is that because they just want the phases for their flux
 
all motors have a neutral. its the sloppy bit on the floor shift, or between P and D on an auto box.
 

Reply to PFC queery in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top