Discuss PFC queery in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
because on 3 phase the pscc is measured between phases ( or L/N ) and pefc is to earth.
hey thanks for the reply i understand that the pscc is between L-N or L-L, but why is this reading higher than that for L-E, i thought that L-E would have a better return path with a lower resistance so consequently would have a higher reading of KA to disconnect the protective device. GN3 claims pscc would be higher but doesnt explain why?
With 3phase, you double the PSCC measured between L&E.
If your instrument is unable to measure the PSCC between phases on a 3P system, as per single phase you measure between L&N.
The PSCC will always be higher between the phases of a 3P system than between L&N because the voltage between them is higher 400 v 230.
The actual sum is to multiply a L-N reading by 1.732 to obtain the theoretical maximum PFC between phases, however we are told to multiply by 2 to err on the side of safety.
Reply to PFC queery in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net