simbin
I did a test yesterday on a new build i've been working on & got a reading of 4.8 kA for PFC. Any ideas why such a high reading, i was expecting lower. Ze was 0.05
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss PFC Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Sounds ok to me then, for future ref if it was above the breaking capacity of your fusing devices then they would either need replacing for higher rated if this cant be done then a device installed upstream (e.g. hrc fuse) which usually have breaking capacities between 16k and 80k.all breakers are 6k, single phase.
I did a test yesterday on a new build i've been working on & got a reading of 4.8 kA for PFC. Any ideas why such a high reading, i was expecting lower. Ze was 0.05