Carried out a ccu replacement and then started testing, my PFC was 38A & 6.11 ohms. Just wanted to have some thoughts as mine was that there must be a poor connection or break in the main cpc?

Thanks
 

Attachments

  • [ElectriciansForums.net] PFC reading
    D1E90D36-5177-4A0A-82A1-0AA60AF32164.jpeg
    1.4 MB · Views: 36
What is the Ze in the property?
 
Did you do any testing before swapping the CU?
 
Carried out a ccu replacement and then started testing, my PFC was 38A & 6.11 ohms. Just wanted to have some thoughts as mine was that there must be a poor connection or break in the main cpc?

Thanks
Presumably that was the Prospective Earth Fault Current (PEFC) as opposed to the Prospective Fault Current (PFC). The Prospective Short Circuit Current (PSCC) must have been substantially greater otherwise the volt drop on the loads would have been enormous to the point where things just wouldn't have functioned.

PFC is the greater of the PEFC and the PSCC.

If it was a TN-S supply then an emergency call to the DNO would be in order assuming that the Earthing Conductor is correctly connected at the MET.
 
No i don’t, and no previous records available
It is advisable to test before carrying out any work to identify any issues and ensure the installation is fit and safe for continued service.

You need to check the main earthing conductor terminations, if at the DNO end you will need to call them out to rectify. What sort of installation is it?
 
Carried out a ccu replacement and then started testing, my PFC was 38A & 6.11 ohms. Just wanted to have some thoughts as mine was that there must be a poor connection or break in the main cpc?

Thanks

Anytime I've had readings like that it has always been down to an external fault on the DNO's side. As Strima mentioed, it is always wise to do your testing before a board change rather than afterwards!
 

Reply to PFC reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
437
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
Very technical :D
    • Like
Replies
9
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top