can anyone tell me when its unnecessary to perform one at each sub-main DB on an installation ?
 
Look at guidance note 3 page 54
Where the the protective devices used at the origin have the neccessary rated breaking capacity,and devices with similar breaking capacity are used throughout the installation,it can be assumed that the regulations are satisfied in this respect for all distribution boards

The reason being, the PFC reduces further down the line in installations
 
i think that i have read that in Sub Mains, if there is a device capable of breaking the pfc upstream then this is ok.
I have this problem at site, due to having a HV ring main, thus being close to transformers (always giving a higher pfc).
 
i think that i have read that in Sub Mains, if there is a device capable of breaking the pfc upstream then this is ok.
I have this problem at site, due to having a HV ring main, thus being close to transformers (always giving a higher pfc).


Just be careful using this reading on bread and butter work as opposed to domestic.
 
When testing in a domestic you only need to put down the PFC for the CU.

When you test a commercial/industrial you have to put doen the PFC for every DB submain within the building as they are on a different test sheet.
 
Last edited:
The pfc for any distribution sub main will be less than the pfc at origin
As long as all protective devices throughout the installation have a rating equal or more than the origin main protective device,then the origin pfc will suffice
 
Last edited:

Reply to Pfc test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
268
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
755

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top