please can someone clarify something for me. when a prospective fault current test is performed at the supply side, is this to make sure that its lower than than, lets say 6ka of the breakers capacity or the supply fuse capacity. the reason i asked this question was i performed this test today on a single phase installation and was getting a reading of 19.9 ka should this be lower than 6ka of the breakers of lower than the supply fuse

cheers
 
What was the result for your Ze? it seems the PFC reading is very high are you close to the supply transformer?
 
please can someone clarify something for me. when a prospective fault current test is performed at the supply side, is this to make sure that its lower than than, lets say 6ka of the breakers capacity or the supply fuse capacity. the reason i asked this question was i performed this test today on a single phase installation and was getting a reading of 19.9 ka should this be lower than 6ka of the breakers of lower than the supply fuse

cheers

Was this domestic ? What type suppliers fuse
19.9 KA is one monster reading for a single phase domestic
Are you absolutely sure of that reading :eek:

You are correct with why the test is done,however
Back up protection by the suppliers fuse (Bs 1361 typeII) covers a domestic installation to 100 amp, the fault protection is by the suppliers fuse on the load side,the consumer units are deemed to have a fault current rating of 16 KA regardless of the mcb ratings


This does not apply in commercial or industrial installations or houses with supplies greater than 100A.
 
sorry mate i forgot to mention its a commercial property, howhever its a single phase supply 100a main fuse bs1361 ans ze is 0.02 ohms
 
so when i test at the origin it should be lower than the supply fuse, lets say 16ka and if im checking at a final circuit it should be lower than 6ka assuming its a bs 60898 type b, am i corect i seem to have forgotten
 

Reply to pfc test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top