m4fiaafg

basically im working on a three phase installation. ive done a pfc test and im getting some abnormal readings. my ze is 0.02 ohms pfc is 19.9ka so times this by two will give me 48.8 ka im assuming that this installation is sitting on a substation hence the low ze, is this reading normal, the main fuse is a bs1361 type 2 please anyone

cheers in advance
 
Last edited by a moderator:
0.02 Ze indicated you are VERY close to the sub station!! what was the PFC readings from all phases???

1361 type 2 has a breaking capacity of 33kA
 
With a Ze of 0.02 the sub-station is not far from your intake, look out the upstairs windows you'll probably be able to see it, if not walk round the area it's got to be close, even allowing for the larger city cables sizes it's definitely going to be in that street or an adjacent one.
 
what difference will nulling leads and how on pfc would u do that its the batts in emlighting i have come accross this and it was always the dbs with em lighting had high pfc but i was not aloud to turn lights out to check but out of 33 dbs it was always the lightin dbs which were high all lighting boards had emlighting aswell.
 
Last edited by a moderator:
This is a question, that I really never got a satisfactory answer to, until I spoke to a ECA auditor. With low Ze reading you get high Ka ratings. Although your overcurrent devices at your main intake DB may not meet PFC values, the overcurrent devices at the service head will. 1361's are rated at 33Ka. In other words in a short circuit situation, and worst case scenario, (at the main DB) the upstream protection will protect the installation. This is accepted as an industry standard, I hope this helps.
 
This is a question, that I really never got a satisfactory answer to, until I spoke to a ECA auditor. With low Ze reading you get high Ka ratings. Although your overcurrent devices at your main intake DB may not meet PFC values, the overcurrent devices at the service head will. 1361's are rated at 33Ka. In other words in a short circuit situation, and worst case scenario, (at the main DB) the upstream protection will protect the installation. This is accepted as an industry standard, I hope this helps.

Perfectly true but only on a single phase 100 A supplies protected by a BS 1361 type II with switchgear to BS 60439-3.

The problem is your meter has abysmal accuracy at values of less than 0.5 Ohms.

By the time you add the transformer winding and the distribution circuit impedance to your supply, it is almost impossible to achieve a genuine Ze of 0.02 Ohms.

We had a similar case on a job at a factory and ended up inserting a resistance into the circuit to lift the meter into it's accuracy 'sweet spot'.

The original measured Ze was 0.03 Ohms, the actual value was closer to 0.06 Ohms!

This looks like an insignificant difference until you look at the effect on fault levels.
 
Can you use A normal resistor for that, or did you use a length of cable?

We used an R2 lead, I wrote a brief guide to the procedure for when we need to use it again (quite often now).

I'll search it out and post it up, in the middle of moving house at the moment so most of my technical stuff has been boxed up by 'er indoors'!
 
Cheers. I had a similar problem a week ago. Measured value of <0.01 on firms megger but 0.06 on my fluke. Maybe fluke compensates for low value? I'd like to try your method though. What's your take on PSCC? On the samejob, I measured phase to phase PSCC less than live to neutral PSCC and PEFC Should I have just multiplied PEFC by 2? It will comply regardless as protected by bs88-2
 
We used an R2 lead, I wrote a brief guide to the procedure for when we need to use it again (quite often now).

I'll search it out and post it up, in the middle of moving house at the moment so most of my technical stuff has been boxed up by 'er indoors'!

I read with interest......
 

Reply to pfc test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
948

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top