Also interesting to note, ...Megger and some other electrical test equipment manufacturers have always been able to supply high resolution loop testers on special order for substation applications and the like. Some now, are making them generally available as part of there range. Although these generally available models will test PFCs to 40KA, the special order models will go to 52kA as i remember...

One such generally available High Resolution model is the Megger LTW425.
 
Thanks for the info IQ, I have a building at the moment with a dedicated Tx, and have a measured value of 0.01 Ohms, will let you know in due course how I make out when adding the resistance of the R2 lead to my 1553.
Kind regards.
 
Hi IQ,
Just a follow up to my last post, I did retry measuring the PFC values of the installation I described in my last post. Went to a remote DB in another part of the building today and measured the Ze of the board. Without R2 wander lead connected Ze 0.20 Ohms-With lead connected 0.80 Ohms, lead resistance 0.60 Ohms. Went back to the main intake-previous reading 0.01 Ohms. With wander lead connected Ze measured 0.61 Ohms. Guess my 1553 must be accurate at very low values. mind you our main intake is next door to the sub station so in reality be only about 5 metres away.
Regards,
Corky 62
 
Hi IQ,
Just a follow up to my last post, I did retry measuring the PFC values of the installation I described in my last post. Went to a remote DB in another part of the building today and measured the Ze of the board. Without R2 wander lead connected Ze 0.20 Ohms-With lead connected 0.80 Ohms, lead resistance 0.60 Ohms. Went back to the main intake-previous reading 0.01 Ohms. With wander lead connected Ze measured 0.61 Ohms. Guess my 1553 must be accurate at very low values. mind you our main intake is next door to the sub station so in reality be only about 5 metres away.
Regards,
Corky 62

Yes, 5 Metres and it probably is correct, some PFC there!
 

Reply to pfc test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top