Hi I know how to test PFC at the origin of the Installation but how do you test PFC at other points in the installation does this mean on the individual circuits like the ends of them, and what about the earthing conductor is it disconnected or connected.and if disconnected why?
 
Hi I know how to test PFC at the origin of the Installation but how do you test PFC at other points in the installation does this mean on the individual circuits like the ends of them, and what about the earthing conductor is it disconnected or connected.and if disconnected why?


Main earth and bonding should all be connected as you want the lowest loop impedances possible (that the parallel paths create) so that you get the highest posssible PFC and you can then select the correct short circuit capacity for the protective device.
 
You want to obtain the Maximum PFC possible so conduct the test at the origin with the earthing condutors and main protective onding condutors connected.

By carrying out at the origin this is the maximum value. Theres no need to conduct the PFC tests for each circuit as this is to determine the short circuit capacticity of the circuit breaker. If needed you can use the value recored at the origin to substitue values of the individual circuis. This is since the PFC will reduce due to the resistance of the circuits so using the PFC at origin will and save you time.
 

Reply to Pfc testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
At this "first" fitting it's loop in. The rest appear to be joint boxes and old par 38 light fittings. It is reasonably old wiring but not...
Replies
3
Views
379

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top