hi ladies and gents,
system= TNS, tranny 5m away on pole, 70mm tails, 3ph
tester= megger 1552
was on a shutdown the other night, and after doing my bit in the main MCC, i did my live tests. i disconnected all bonding and earthing conductors, and took my readings. ZS is 0.01, which i expected and PEFC measured at > 20ka (calculated at 24.5 kA). same reading for PSCC (calculated at 24.5 x 2 = 49kA).
from this MCC, i installed a 63A switchfuse fed by 25mm2 tails from busbar, which feeds a 25m run 25mm2 SWA to the VSD panel for 2 pumps.
When testing Zs for the VSD panel i got 0.02.
PEFC was 7.2Ka and as the megger allows testing between phases, i measured that too, but got 5.5kA?
why was this? all phases tested frine on R1+R2 same readings (0.05) and Zs was the same on all too, (0.02).
I was taught that on a TNS, PSCC on a 3ph system will always be higher than PEFC?
did i even need to test PSCC and PEFC at the VSD panel? i did it anyway. would the fuses (63A, bs 88-2) discriminate at those currents, or would it take out the 200A main fuses in the main MCC also?
thanks in advance for your advice
John
system= TNS, tranny 5m away on pole, 70mm tails, 3ph
tester= megger 1552
was on a shutdown the other night, and after doing my bit in the main MCC, i did my live tests. i disconnected all bonding and earthing conductors, and took my readings. ZS is 0.01, which i expected and PEFC measured at > 20ka (calculated at 24.5 kA). same reading for PSCC (calculated at 24.5 x 2 = 49kA).
from this MCC, i installed a 63A switchfuse fed by 25mm2 tails from busbar, which feeds a 25m run 25mm2 SWA to the VSD panel for 2 pumps.
When testing Zs for the VSD panel i got 0.02.
PEFC was 7.2Ka and as the megger allows testing between phases, i measured that too, but got 5.5kA?
why was this? all phases tested frine on R1+R2 same readings (0.05) and Zs was the same on all too, (0.02).
I was taught that on a TNS, PSCC on a 3ph system will always be higher than PEFC?
did i even need to test PSCC and PEFC at the VSD panel? i did it anyway. would the fuses (63A, bs 88-2) discriminate at those currents, or would it take out the 200A main fuses in the main MCC also?
thanks in advance for your advice
John