Take the BS 88 as your up stream, Breaking cap 80 Ka
now if you have a high pfc(50Ka) let say at the terminals of a 15ka rated Mccb, the let through energy of the bs 88 may be say 20 ka, so the mcb needs to be of a higher rating.
The pfc need to be calculated at each point back up protection may be provided by an upstream device, though this would need to be calculated and not assumed.
So down stream devices need to be able to break the 20 ka