Indeed this conversation is going beyond the realms of normal sparkies, perhaps we can continue in the pub 'lol'
anyway good work
 
Take the BS 88 as your up stream, Breaking cap 80 Ka

now if you have a high pfc(50Ka) let say at the terminals of a 15ka rated Mccb, the let through energy of the bs 88 may be say 20 ka, so the mcb needs to be of a higher rating.

The pfc need to be calculated at each point back up protection may be provided by an upstream device, though this would need to be calculated and not assumed.

So down stream devices need to be able to break the 20 ka
never heard them terms before
.....chris and your qualifications are??
 
Well if your measuring the L - L, Zs = The line to line loop

so 400/ Zs + 2R1

Now i used the Three phase calculation Where ZS is the Line neutral loop as that was what i assumed you tested.So ill try again lol.

245 x 1.73 = 423 v L - L, 245/24500 = .01

R1= .022


So 400/1.73 divided Zs .= .01 + R1= .022 = 7656.25amps

For the line to line calculation at mcc we would need to know the PSCC where ZS = the line to line loop not the line to neutral loop.

Ill remove my earlier post, heavy question for a sunday lol
 

Reply to Pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
260

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top