But it can't be -can it?? Ze & PEFC are measured in completely different ways.
Did you not read my earlier post??
They can be the same. I measure them at the calculation values every day of the week.
It's on a test rig, where the main bonds are connected to a 200mm piece of copper that provides no different potential what-so-ever.
They don't go anywhere near the floor though
So as not to confuse the 'learners' - who were mentioned before.
If you had a warehouse supplied by a single phase TN-C-S system and your measured Ze was 0.35 ohms.
By the calculation the PEFC would be 230/0.35 = 657 Amps.
But there are a load of 'bonded' metal supports for this warehouse, which give a Zs at the Distribution Board of 0.2 ohms...........giving a measured PEFC of 1150 Amps (1.15 KA).......because PEFC is measured with the 'bonding 'connected.
A bit of a difference, wouldn't you agree?
A bit of a difference, wouldn't you agree?
???So as not to confuse the 'learners' - who were mentioned before.
Yes but you said it couldn't be calculated.If you had a warehouse supplied by a single phase TN-C-S system and your measured Ze was 0.35 ohms. By the calculation the PEFC would be 230/0.35 = 657 Amps.
Correct but Ze is measured at the DB where the PEFC is 657. As you have done what I said - Uo/Ze.But there are a load of 'bonded' metal supports for this warehouse, which give a Zs at the Distribution Board of 0.2 ohms...........giving a measured PEFC of 1150 Amps (1.15 KA).......because PEFC is measured with the 'bonding 'connected.
Yes but they are all PEFCs.A bit of a difference, wouldn't you agree?
Not at the DB. Is that where you're confused?.because PEFC is measured with the 'bonding 'connected'
I would expect this is probably due to EWR regulation 14 again
Bloomin thing.
Work on or near live conductors
14. No person shall be engaged in any work activity on or so near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless–
(a)it is unreasonable in all the circumstances for it to be dead; and
(b)it is reasonable in all the circumstances for him to be at work on or near it while it is live; and
(c)suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury.
This thread has made me think - damn!
My meter doesn't do it, but you know the meters that advertise that they give you simulltaneous Ze and PEFC readings on the screen............they must be using Ze in the calculation then???
Not at the DB. Is that where you're confused?
.........but Ze is measured at the DB where the PEFC is 657. As you have done what I said - Uo/Ze.
At fixtures PEFC is Uo/Zs.Yes but they are all PEFCs.