Hi Guys,

Came accross an install today where a new 2 way board has recently been installed to make room for a new shower circuit (Db1 - 16th edition full board).

How the 'electrician' had wired it was by using 16mm tails from DB1 main switch which now has 25mm and 16mm crammed in there (please note there are no cores cut). I no this is not the correct way but now the customer is asking which regulation this does not conform too (basically I don't think he trusts me).

The main service fuse was marked up as a 1361 type ll 60amp.

Can somebody please shine some light on this please, I don't think ill be reattending to split the tails with a henley block anytime soon :p

Thanks
 
I no this is not the correct way but now the customer is asking which regulation this does not conform too
tell the customer that the rules are has follows .
1) get the numbty to come back to put the tails in tail block.
2)over crowding the manufactures instalment of the isolator.
3) putting a strain on the isolator .
4) walk from the job and tell him you will not be back.
 
Last edited:
Could try and use 434.3.iv

Then advise that the DNO stipulates the tails installation be changed to meet thier requirements - may only apply to DNO tails but let's not split hairs, customer wants a reg number and you've now got one.
1581781931798431727967.jpg
 
I'm not sure there is. More likely its what the manufactures instructions would say. I'm thinking of the internal fly leads for feeding RCD's, with the welded cable ends. You can put more than one cable in an mcb. Not that I would try & put two large diameter cables in one terminal.
 
It comes down to engineering judgment really doesn’t it.....you can run 2 radials or both legs rfc from an mcb but realistically you wouldn’t start adding more circuits for practically.....I can’t imagine that main switch with a 25 and 16 mm cable in it is clamped down to well?
 
If it's done with care I cant see a problem, the only regulation breached might be the requirement to take into account manufactures instructions, who will stipulate a maximum conductor size for the terminations.
However if the connections are tight, secure and how no signs of thermal damage then I feel it's bordering on 'Jobsworth' territory to insist it's changed. If the above applies I would just note it on the comments box of my cert.
[automerge]1581792620[/automerge]

4) walk from the job and tell him you will not be back.
If we all 'walked' every time there was a non compliance on an existing installation which a client was reluctant to spend money on nothing would get done.
Ridiculous post.
 
If we all 'walked' every time there was a non compliance on an existing installation which a client was reluctant to spend money on nothing would get done.
Ridiculous post
the op has pointed out to a customer that the 25+16=41 mm tails are put in a
isolator ,and there for the design are made for 25mm tails not 41 , you could get away with it many years ago, but not like the olds wylex isolators with a couple of screw to terminate the tails .
 
the op has pointed out to a customer that the 25+16=41 mm tails are put in a
isolator ,and there for the design are made for 25mm tails not 41 , you could get away with it many years ago, but not like the olds wylex isolators with a couple of screw to terminate the tails .
I didn't say it was compliant, but if the OP is carrying out other work and the customer does not want him to remedy this, he just needs to verify that the connection shows no sign of thermal damage, and is secure and tight.....and note exactly that on his cert.
Walking away because of a relatively minor deviation from the regulations which does not form part of the work being carried out is plain daft.
 
While I accept this sort of thing is not uncommon and even allowed in regs subject to having a fault protection capable of protecting the cable to the sub-main, the question would arise what is the main fuse? For 16mm tails let's hope it's not 100A! But then I imagine taking in to account manufacturers installation instructions most of us would baulk at doing this as we would not comply with said instructions, wouldn't we? I personally don't like putting different size cables in the same termination due to difficulties in securing a good termination.
 
@digital_boy You could refer to regulation 462.1.201 "A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation."
 

Reply to 'Piggy backing' tails in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top