S

sid578

hi .doing a test on a complex where the tails are 25mm ..main bond 16mm ..but the cable bonding main water is only 6mm..think the tails have been upgraded from original but not water bond (not a easy run) .there are 30 flats in complex ..what pir code would i put fo this
 
use adiabatic equation to determine the min. reqd. size for main earthing conductor. ( irrespective of the fact that the re is a 16mm there). then the main bonding conductor/s need to be at least 50% of that size.
 
As there's existing bonding, assuming it's metal and extraneous. TNC-S = minimum of 10mm, it is potentially dangerous, so code 2.
 
The reason for the minimum sizes (and why they must be updated before any work is done) is to ensure that fault current can be handed in the event of a fault. It would depend on where the fault was (which circuit/ocpd etc) to actually cause a real issue.

If it isn't potentially dangerous, why would it need to be upgraded before any work was done?
 
The reason for the minimum sizes (and why they must be updated before any work is done) is to ensure that fault current can be handed in the event of a fault. It would depend on where the fault was (which circuit/ocpd etc) to actually cause a real issue.

If it isn't potentially dangerous, why would it need to be upgraded before any work was done?

Not picking a fight BUT if it was this important why don't those who make the rules, make any attempt to educate the public. More often than not Joe Public thinks that the sparkie is trying it on with unnecessary work.

Joe Public would say his cables on his final ring have 1.5mm earth so what's wrong with his 6mm bonding.
 
that's 4.62 for the main earthing conductor. you can divide that by 2 for bonding. for pme, though 10mm is specxified, so a C3, IMO. there's no code 4 now.
 
In comment to telex and top quark i'd split the difference
C3 if undamaged and soundly connected , C2 if heat damaged and badly connected.
This is new diplomatic biff.
;-)
 

Reply to pir code for undersizes water bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top