went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?

1. no earth connected to metal light fitting. earth in cable but not on light.
2. twin and earth cable in roof space. property being thatched roof no rodent protection.
3. no 30ma rcd protection to ground floor sockets. socket could be used outside.
4. no fan isolator in downstaires toilet. no window
5. socket over cooker. plug lead over above hob on double socket.
6. cooker cable not clipped to surface from isolator to switch.
7. no main earth bond on oil pipe.

The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property.

going back tomorrow so will find out what the electricity company say.

what codings would everyone say the points are.

thanks.
 
went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?

1. no earth connected to metal light fitting. earth in cable but not on light. code 2
2. twin and earth cable in roof space. property being thatched roof no rodent protection.not compliant with effect of externall influences, IMO code 4.
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. code 1 for outside sockets
4. no fan isolator in downstaires toilet. no window. isolator not obligatory. no code
5. socket over cooker. plug lead over above hob on double socket.code 2 IMO
6. cooker cable not clipped to surface from isolator to switch. unsure where you mean. code 4?
7. no main earth bond on oil pipe.code 2 if the pipe is metallic and comes from outside

The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property. see what they say. if no chance of pme, then you'll have to TT it

going back tomorrow so will find out what the electricity company say.

what codings would everyone say the points are.

thanks.

my commentsa are my personal opinion and could be altered with an appropriate amount of the amber nectar
 
Last edited:
went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?

1. no earth connected to metal light fitting. earth in cable but not on light. Code 1 IMO
2. twin and earth cable in roof space. property being thatched roof no rodent protection. Possibly 4 but maybe just an Observation
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. Code 2
4. no fan isolator in downstaires toilet. no window No code
5. socket over cooker. plug lead over above hob on double socket. Probably no code
6. cooker cable not clipped to surface from isolator to switch. Code 2
7. no main earth bond on oil pipe. Code 2

The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property.

going back tomorrow so will find out what the electricity company say.

what codings would everyone say the points are.

thanks.

PIR codes Always opens up debate!!
 
true, but i stand on code 2 for the cpc not connected to light ( not a real and immediate danger), and code 1 or 2 for the socket can be used outside. we're mostly in agreement though.
 
I base my codes on the set ones givem to be by our companys I&T department, although I certainly see that the metal fitting presents no immediate danger, so I certainly wouldn't argue with a 2.
Sockets not on RCD I'm given the choice of putting 4, which I use where sockets are upstairs/unlikely to be used outside and 2 if they downstairs/near doors.

My personal favourite solution, which I have seen once or twice is stickers stating 'not suitable for equipment outdoors stickers' lol
 
went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?

1. no earth connected to metal light fitting. earth in cable but not on light. ( code 2)
2. twin and earth cable in roof space. property being thatched roof no rodent protection. (no code )
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. (code 4)
4. no fan isolator in downstaires toilet. no window (no code)
5. socket over cooker. plug lead over above hob on double socket. ( no code )
6. cooker cable not clipped to surface from isolator to switch. ( not sure what you mean exactly)
7. no main earth bond on oil pipe. ( code 2)

The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property.

going back tomorrow so will find out what the electricity company say.

what codings would everyone say the points are.

thanks.



cant see why sockets eithout rcd would be code 1 or 2 unless it is a TT
 
cant see why sockets eithout rcd would be code 1 or 2 unless it is a TT

generally a code 4. however, if able to be used outside, i believe a code 2 is more appropriate because of the increased danger.
 

Reply to PIR coding help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top