i would certainly recommend an RCD socket and state that in the comments.
 
The bonding as your earth to me is a 2.
Light CPC is a 3
No RCD is a 4
T+E in roof is a 3
And is the no isolator in a TOILET or BATHROOM.
 
Last edited by a moderator:
What I mean by non rcd sockets is the ground floor sockets could be used for a extension lead and lawn mower. The installation gas a 100amp 100ma rcbo switch.

the cooker has a double socket over the hob wich the hood plugs into. maybe a danger with lead over the hob.

Thanks
 
went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?

1. no earth connected to metal light fitting. earth in cable but not on light. Code 2
2. twin and earth cable in roof space. property being thatched roof no rodent protection. No code
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. Code 2 (or code 4 100mA RCD is useful probably not a very bad shock)
4. no fan isolator in downstaires toilet. no window No code
5. socket over cooker. plug lead over above hob on double socket. Code 2
6. cooker cable not clipped to surface from isolator to switch. Code 4
7. no main earth bond on oil pipe. Code 2

The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property. Something you should discuss with customer first unless you have been told to do all remedial works, PIR is recommendation not action. Certainly a good idea but may well cost.

going back tomorrow so will find out what the electricity company say.

what codings would everyone say the points are.

thanks.
Nothing requires further investigation so no code 3s.
 

Reply to PIR coding help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top