HI all,

dont really do PIR's but its family,

basically its and 30+ house they want to sell , wiring in good condition

earth in lighting

old WYLEX board with, 6mm main earth, 6mm to water and gas.

no rcd protection, TN-C-S

ok, so is it satifactory or not, i know its not upto 17th Ed regs but was fine when installed so it comply's yes.?


never sure on these as my house has a 16th Ed board in and would be satisfactory , where do you draw the line. to me no RCD and it should be changed.?

there was a big debate on the tv cowboy programme as there was and old wylex rewire-able board in 6mm earth to water and gas, basically every spark told them they needed a new board, which quite honestly i would have recommended, but expert said even that it comply's yo BS7671, so i never know

thanks
Grand
 
all code 3's, so a satisfactory report, IMO. i would only add a code 2 for no RCD/s if sockets used for outside portable equipment.
 
Last edited:
It doesn't comply with the 17th ed bs7671 but may have complied with a previous edition, as long as it is serviceable and not dangerous just advise not to current regs.
 
No rcd protection to bathroom circuits and sockets for outdoor use as a minimum.

If supplementary bonding in place (not confirmed) then this conformed to a previous version of regs and so would not contribute to a non-satisfactory conclusion. Rcd protection of sockets is 16th so if this was done before the 16th then again ok! but would 'recommend' RCD installed or at least use an RCD plug.
 
See this is where it all falls down abit. im concerned about the bathroom no RCD, but then it was ok when first installed so there is nothing wrong with it, personally if i go to a property and look at the immersion heater, if it hasnt got a thermal cutout on it as this installation hasnt i would code that a code 1.

im filling in a visual report, i took a socket off and all was fine and unscrewed a few pendants saw earth and all looked ok.

the thing is if i walk in a house to do any type of work i insist on a new board.but im not in this case.

thanks for the replys lads
 
See this is where it all falls down abit. im concerned about the bathroom no RCD, but then it was ok when first installed so there is nothing wrong with it, personally if i go to a property and look at the immersion heater, if it hasnt got a thermal cutout on it as this installation hasnt i would code that a code 1.

im filling in a visual report, i took a socket off and all was fine and unscrewed a few pendants saw earth and all looked ok.

the thing is if i walk in a house to do any type of work i insist on a new board.but im not in this case.

thanks for the replys lads

Thats too sweeping a statement for me to accept,after all, safety is not something that was first dreamed up when the 16th and 17th editions came about
Admittedly,the use of Rcds tend to make systems safer,but thats generally where they were unsafe for the editions they were installed to in the first place
 
i would not insist on a new board, but obviously i would have to RCD any work i did, and also ensure earthing and bonding were adequate, or uypgrade.
 
Understand some of the comments, but just beacuse something was fine at the time does not mean that it is acceptable now. When you do your periodic you assess to the current edition of the regs.
 
Understand some of the comments, but just beacuse something was fine at the time does not mean that it is acceptable now. When you do your periodic you assess to the current edition of the regs.

If that was the case, then every PIR on an installation pre 17th edition, would be deemed unsatisfactory !!
 
Last edited by a moderator:

Reply to PIR is it satisfactory.? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
490
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
354

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top