If when u have carried out a pir and the installation is unsatisfactory and u have recommended a re wire on some circuits or all what do u put on the label on the fuseboard if you u are saying it needs re wiring on the cert to say next inspection in 5 years does really make sense as you are saying it needs attention straight away ? Any ideas what do u do ?
 
It always for me depended on how many codes 1 + 2 you found. If the installation was so bad that it needed a rewire then I may not attach a sticker at all and inform the client in writing that IMO it was in need of rewire and therefore I would not recommend another inspection date as it pointless to re-inspect. You can also high light this on your PIR in the "next inspection" section

I have never done this to be fair, the shortest period I did was a 6 month one, for a commercial site, where I carried quite a bit of remedial work, once I had completed the work I replaced that sticker with a 5 year one, and then issued another PIR with the 5 yrs on it. This was recommended due to there being quite a lot of old MICC cable that were IMO starting to breakdown as they have fairly low IR readings.
 
How about 'N/A-See PIR Serial No. XXXX'

In line with ESC recommendations, we avoid making statements like 'needs a rewire' and instead would use something like 'from the measured test results, it would appear that the installation has reached the end of it's safe working life'

By the same token, it's best not to describe a 'satisfactory' installation as 'good' or 'excellent' but merely 'acceptable'

I know it sounds pedantic but it covers your Arsenal ;)
 

Reply to Pir label on board in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
No it is not implying it is safe, it is stating what the recommended date for the next inspection is. The next inspection date sticker doesn't...
Replies
10
Views
2K
davesparks
D
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top