SSE are you saying there is a main protective bonding conductor going from the MET to a clamp on the gas pipe next to the meter and then another bonding conductor going from a point 6M along the gas pipe to the incoming water pipe?
If so there are two issues; 1, the fact that the main bonding conductor is not continuous so that the removal of one bond to an extraneous conductive part (gas) could cause another connection to an extraneous conductive part (water) to be open/disconnected 528.3.3 There is no regulation in BS7671 that specifically requires the bonding conductor to be void of any permanent joints, ie soldered, brazed or crimped joints deemed to be permanent. So the guy who said crimping the two bonding conductors at the midpoint of the main bonding conductor sounds OK to me.
Point 2 is only if the two BS951 bonding clamps are 6M apart on the gas pipe. 543.2.1 a gas pipe shall not be selected as a protective (bonding) conductor
 
SSE are you saying there is a main protective bonding conductor going from the MET to a clamp on the gas pipe next to the meter and then another bonding conductor going from a point 6M along the gas pipe to the incoming water pipe?
If so there are two issues; 1, the fact that the main bonding conductor is not continuous so that the removal of one bond to an extraneous conductive part (gas) could cause another connection to an extraneous conductive part (water) to be open/disconnected 528.3.3 There is no regulation in BS7671 that specifically requires the bonding conductor to be void of any permanent joints, ie soldered, brazed or crimped joints deemed to be permanent. So the guy who said crimping the two bonding conductors at the midpoint of the main bonding conductor sounds OK to me.
Point 2 is only if the two BS951 bonding clamps are 6M apart on the gas pipe. 543.2.1 a gas pipe shall not be selected as a protective (bonding) conductor

Coming from the consumer unit to the gas meter, main point of entry there is a 10mm earth run to it that is clamped onto the gas pipe. From this gas meter the pipe which the earth is clamped on, runs about 6m to the back of the house where the boiler is and the main incoming water service. Then there is a 10mm earth that is clamped from the gas pipe to the water to each of the other pipes beside it.
 
Point 2 is only if the two BS951 bonding clamps are 6M apart on the gas pipe. 543.2.1 a gas pipe shall not be selected as a protective (bonding) conductor

but then look at 543.2.2 (viii). and 543.2.6
 

Reply to PIR question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

  • Article
This is an RSS feed of thread: Gas or Water Pipe? Look to find cause of damp in wall. Content of the thread: Hi all, First time post so please...
Replies
0
Views
188
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top