I'm doing a domestic PIR for rental purposes and fixing things as I go along (I'm not working to Amend No 1 yet). There are some things I can't fix. A lighting circuit with insulation resistance L-E 300k, hidden junction boxes -both Code 3. Code 4s - no grommits, switch wires unsleeved, cable sheaths not in boxes. A farmer's DIY job. It's all RCD protected. Zsssss are fine.
Best Practice Guide No 4. says that where a code 3 is justified, I have to'exercise judgement as to whether the overall assessment of the condition of the installation should be indicated as satisfactory or unsatisfactory.
I think it's unsatisfactory, but safe. Problem is that the tenants are moving in tomorrow!
What would you do?