Hi people

I had an high Zs of 0.85 on a 32 Amp type C ring circuit, which was on an RCBO. My first thought was to give it a code 2 'requires improvement', and then change it to a type 'B' so it would conform. Then I thought it is on an 30mA RCBO, where the max Zs in theory can be 1667 ohms. Just asking what you guys would do and why.
 
Is that not something different as the neutral is not part of the ZS loop.

CNE? or PEN?

On a line to neutral fault it would be the PSCC which would blow the MCB

Indeed, though if we have three conductors all the same csa Neutral and Earth connected at the link, if we have a high Zs then we could also assume a high L -N loop reading.

Ive seen A very similar thread somewhere else:)
 

Reply to PIR Test high Zs on 32 Amp RCBO in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top