for what reason is it on a type C?. if no need for it, fit a type B.
I want to know if a 'C' will conform as it is on a RCBO.
for what reason is it on a type C?. if no need for it, fit a type B.
Well if its been designed so that the rcd gives earth fault protection, then the Zs is acceptable
what about Phase to Neutral faults?
sorry to say that last statement is wrong....page 49 of brb says type c requires 0.72 max zs to operate in required time to protect cable...type b requires 1.44 ohms, so as many others have said before change to a type b....unless there's a good reason not to
what do you say that then IQ??sorry to say that last statement is wrong....page 49 of brb says type c requires 0.72 max zs to operate in required time to protect cable...type b requires 1.44 ohms, so as many others have said before change to a type b....unless there's a good reason not to
what do you say that then IQ??
excellent thank youI say refer to post 21 where it is summed up perfectly.
You are not using the overcurrent protective device to meet disconnection times, you are using the RCD.
an rcd does nothing to protect against overcurrent, which is the the thing you are trying to avoid by having a good continuity measurement...too high a continuity will delay tripping which could result in cables melting.....
an rcd does nothing to protect against overcurrent, which is the the thing you are trying to avoid by having a good continuity measurement...too high a continuity will delay tripping which could result in cables melting.....
There is a good reason not to.....an RCD can be used to provide earth fault protection,as the protective device incorporates an RCD a max Zs of 1667 ohms applies.....you are incorrect....
Reg 411.4.9 and table 41.5