PIR Test high Zs on 32 Amp RCBO

Well if its been designed so that the rcd gives earth fault protection, then the Zs is acceptable

Perfectly true, once continuity of protective conductors is confirmed, Zs is almost superfluous.
 
sorry to say that last statement is wrong....page 49 of brb says type c requires 0.72 max zs to operate in required time to protect cable...type b requires 1.44 ohms, so as many others have said before change to a type b....unless there's a good reason not to
 
sorry to say that last statement is wrong....page 49 of brb says type c requires 0.72 max zs to operate in required time to protect cable...type b requires 1.44 ohms, so as many others have said before change to a type b....unless there's a good reason not to

There is a good reason not to.....an RCD can be used to provide earth fault protection,as the protective device incorporates an RCD a max Zs of 1667 ohms applies.....you are incorrect....
Reg 411.4.9 and table 41.5
 
Last edited by a moderator:
sorry to say that last statement is wrong....page 49 of brb says type c requires 0.72 max zs to operate in required time to protect cable...type b requires 1.44 ohms, so as many others have said before change to a type b....unless there's a good reason not to
what do you say that then IQ??
 
what do you say that then IQ??

I say refer to post 21 where it is summed up perfectly.

You are not using the overcurrent protective device to meet disconnection times, you are using the RCD.
 
an rcd does nothing to protect against overcurrent, which is the the thing you are trying to avoid by having a good continuity measurement...too high a continuity will delay tripping which could result in cables melting.....
 
What garbage, you think you need 'good continuity' for overcurrent protection?

I'm out.
 
an rcd does nothing to protect against overcurrent, which is the the thing you are trying to avoid by having a good continuity measurement...too high a continuity will delay tripping which could result in cables melting.....

Think you need to do some reading up mate.


Sent from my iPhone using Tapatalk.
 
an rcd does nothing to protect against overcurrent, which is the the thing you are trying to avoid by having a good continuity measurement...too high a continuity will delay tripping which could result in cables melting.....

411.4.9.....an RCD for earth fault protection is used as well as overcurrent protection.
435.1 ....A device meeting the requirements for overcurrent protection will also meet the requirements for fault protection.
 
There is a good reason not to.....an RCD can be used to provide earth fault protection,as the protective device incorporates an RCD a max Zs of 1667 ohms applies.....you are incorrect....
Reg 411.4.9 and table 41.5

dual rcd splitload board. 30ma. you dont have to meet the maximum ZS calculations for each circuit @ 80% because you also have an RCD? is that correct??? thanks
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Guest 004,
Last reply from
jamie-spark,
Replies
34
Views
8,844

Advert

Back
Top