am currently doing a pir on some flats, and need some help on a fault code. In the basment their is 4 bs88 isolators off the supply, which feed the 4 flats, the submain to each flat is a 10mm TE with no seperate earth, which means earth is undersized, correct? 1,2 or 4? falutcode as its 4mm. Also the bs88's are 100a which exceeds the rating of the cable, is this a 1,2? thanks
 
incorrct sized earthing is usually a 2, same with the overrated fuse for the cable UNLESS there are signs of overheating etc
 
am currently doing a pir on some flats, and need some help on a fault code. In the basment their is 4 bs88 isolators off the supply, which feed the 4 flats, the submain to each flat is a 10mm TE with no seperate earth, which means earth is undersized, correct? 1,2 or 4? falutcode as its 4mm. Also the bs88's are 100a which exceeds the rating of the cable, is this a 1,2? thanks

Read Regulation 543.1.1 before you put on code down for that CPC.

The incorrect size of the protection device can be a 2 yes.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
pir testing flat, fault code
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
graham123,
Last reply from
Octopus,
Replies
6
Views
2,203

Advert

Back
Top