graham123

am currently doing a pir on some flats, and need some help on a fault code. In the basment their is 4 bs88 isolators off the supply, which feed the 4 flats, the submain to each flat is a 10mm TE with no seperate earth, which means earth is undersized, correct? 1,2 or 4? falutcode as its 4mm. Also the bs88's are 100a which exceeds the rating of the cable, is this a 1,2? thanks
 
am currently doing a pir on some flats, and need some help on a fault code. In the basment their is 4 bs88 isolators off the supply, which feed the 4 flats, the submain to each flat is a 10mm TE with no seperate earth, which means earth is undersized, correct? 1,2 or 4? falutcode as its 4mm. Also the bs88's are 100a which exceeds the rating of the cable, is this a 1,2? thanks

Read Regulation 543.1.1 before you put on code down for that CPC.

The incorrect size of the protection device can be a 2 yes.
 

Reply to pir testing flat, fault code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
525
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
758
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top