hi guys sorry if this has come up before but i am a bit confused with some advice i got given from nic. when carrying out periodic inspection reports i was not recording a unsatisfactory if the client did not have rcd. I was putting this down as 4 noting that it did not comply with the latest wiring regs. But the nic said i should be failing these and recording them as a 2 unsatifactory. Are the rest of us doing this ?thanks for reading guys.
 
hi guys sorry if this has come up before but i am a bit confused with some advice i got given from nic. when carrying out periodic inspection reports i was not recording a unsatisfactory if the client did not have rcd. I was putting this down as 4 noting that it did not comply with the latest wiring regs. But the nic said i should be failing these and recording them as a 2 unsatifactory. Are the rest of us doing this ?thanks for reading guys.

Examle for PIR on 16th edition installation.
Sockets that may be used for outdoor use generally ground floor with no RCD then unsatisfactory code 2.
Sockets for indoor general use with no RCD then satisfactory code 4.
Cables concealed in walls etc with no RCD then satisfactory code 4.

Check out best practice guide 4 Best Practice Guides | Electrical Safety Council
 
hi guys sorry if this has come up before but i am a bit confused with some advice i got given from nic. when carrying out periodic inspection reports i was not recording a unsatisfactory if the client did not have rcd. I was putting this down as 4 noting that it did not comply with the latest wiring regs. But the nic said i should be failing these and recording them as a 2 unsatifactory. Are the rest of us doing this ?thanks for reading guys.

interesting.

Nic man is correct

i fail these items as code 2 because the use of the RCD in the new 17th regs is a fundamental SAFETY requirement now.

just like outdoor sockets needed RCD in 16th edition. Now pretty much all circuits need it. Its the same fundamental safety issue. we are not talking a change in cable colours here...or some other minor harmonization issue. its protection against electrocution! people have been injured / killed after drilling through a non RCD protected cable and so yes these deviations should be cat. 2
 
So, if the original installation met the regs at the time it was put in, it must have been safe. So why is it now unsafe?? Look at it this way. There are a lot of vintage cars on the road, they do not meet current regulations, but they are not scrapped, are they? No. So, if the installation does not meet the current regs, then its a code 4.

Steve.
 
if a car passes an mot reguardless of age then its fit for the road. if an electrical installation does not meet current regs then it has to be upgraided to do so thats the way i see it or whats the point of having them.
 
interesting.

Nic man is correct

i fail these items as code 2 because the use of the RCD in the new 17th regs is a fundamental SAFETY requirement now.

just like outdoor sockets needed RCD in 16th edition. Now pretty much all circuits need it. Its the same fundamental safety issue. we are not talking a change in cable colours here...or some other minor harmonization issue. its protection against electrocution! people have been injured / killed after drilling through a non RCD protected cable and so yes these deviations should be cat. 2

code 4 does not comply with bs 7671 2008
if it complies to when it was installed its a code 4
are you saying any install done before 2008 is a code 2 ?
 
when the installation was done it would have been to current regs so no codes nesessary i would code 2 unprotected bathrooms/ and sockets .but thats the problem with 7671 with it been a non statuary document there just too many grey areas for me. thats why you have to be very carefull when doing a pir cos where theres blame theres a claim and your name is on the bottom of it.
 
calv,

When I had my van MOT'd the other day, it passed but I had a couple of advisories. Surely this is what the pir is, an electrical MOT. It would be nice for us that, when the regs change, the phone rings off the hook with people wanting to upgrade :) But we all know this does not happen!!

Agree with the bathroom etc. I always make a note that although it does not comply, it would be a good idea to upgrade it.

Steve.
 
The PIR is a report that is used to monitor the installation to confirm that the protective measures used for that original installation have not deteriorated and remain as effective as when they were first installed

It is not a requirement to upgrade every installation that has been installed to a previous edition
Observations and recomendations to bring the installation up to current standards are common sense actions

If there are such things as lack of RCD protection,then the installation which was wired to a previous edition and now no longer meets the current standards,just because the standards have changed,it does not suddenly render that installation as dangerous
Coding that change should take account of whether there is immediate danger or urgent attention that has aisen
To my understanding neither of those 2 statements are relevant for this,so the coding I would give would be 4

The NIC/ESC has come up with advise that any code 2 should warrant an unsatisfactory
I believe they are completely out of touch with practicality and common sense
eg Absense of RCD protection for portable appliance or equipment that may be reasonably be expected to be used outdoors
Now this is definitely not covered by any immediate or urgent danger
Because the fixed wiring did not have this in its original safe installation then that fixed wiring suddenly becomes dangerous?
The RCD requirement is an add on from previous editions and can be overcome by using a plug in RCd
To unsatisfactory the system because of such a change when the basic protection remained satisfactory is wrong,recomending bringing that installation up to standard whilst being satisfactory should be the approach
 
oh ok so..

BS 7671 says

bathrooms deifinately need 30mA RCD's ...everyone agrees yes yes thats definately a code 2

sockets feeding outdoor equipment definately need 30mA RCD's yes yes everyone agrees code 2.

BS 7671 also says the same life saving 30mA RCD should now be protecting all sockets and in some cases concealed cables


but hang on!!... oh no no no.. thats ridiculos.. thats a differnt sort of 'potentially dangerous'. hmmm surely we cant recommend that this should be improved?? no no its only a code 4 !!

fickle or what?!

this is not just minor change in the book like cable colours. these are fundamental safety changes to protect people in the home that the rest of europe has had in place for a decade. No one is saying that installation pre 2008 are unsafe. they are however potentially dangerous especially if some one drills through a cable or a kiddy messes around with a socket or appliance and gets electrocuted.

i class that as code 2 - requires improvement.why wouldn't an inspector wish to improve on that?
 
look up definition of 'guidance note'

i garantee that in ten years time when all this RCD excitement is finished and its common knowledge to expect a circuit to be safely protected by a 30mA RCD.. all PIR's will have code 2's releting to this issue. You can keep putting in lazy code 4's for the next 50 years is you want to..where do you draw the line? when will it dawn on you that actually maybe it should have an RCD like every other circuit in the country? For safety reasons!!

Can we clarify if all we are talking about here is domestic only and not commercial / industrial


obviously
 
Last edited by a moderator:
Initially I was puttign code 4 on the no RCD installations but an now putting code 2 on the basis that this says it is not meeting current safety standards, which are higher than the standards that were required a few years ago. I explain to the customer the reasoning behind whay I say this as well and they generally accept it as sensible even if they choose to do nothing about it.
 
look up definition of 'guidance note'

i garantee that in ten years time when all this RCD excitement is finished and its common knowledge to expect a circuit to be safely protected by a 30mA RCD.. all PIR's will have code 2's releting to this issue. You can keep putting in lazy code 4's for the next 50 years is you want to..where do you draw the line? when will it dawn on you that actually maybe it should have an RCD like every other circuit in the country? For safety reasons!!




obviously

Just wanted to clarify it was domestic and not commercail as it makes a difference as to whether RCD protection would be required or not.
 

Reply to pir in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
415
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
729
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
966

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top