Hi all, 2nd year apprentice.

I'm looking to take a supply out to my garage, which is detached, from the DB at the front of the house (2 bed terraced, built 1978~)

The length of run is about 30m (having to go through either loft or under floorboards).

Intend to have a 20A radial and a 6A lighting circuit so am I right in thinking I'd allow 66% diversity for lighting and 50% for the power circuit as it's over 10A? So 13.96A total demand?

Thanks 😊
 
Here is the swa being ran to the garage
 

Attachments

  • [ElectriciansForums.net] Planning garage sub-main project
    20230620_184643.jpg
    666 KB · Views: 42
The right hand side of your board with the lighting MCBs isn't RCD protected and the blank will be a spare way- so subject to a decent Ze you could simply fit an additional matching MCB for the new SWA, but it will have to be glanded properly, possibly into a small metal enclosure to ensure the armour is earthed. EDIT= Ah I've just seen your post stating T&E for the first part of the run, so the SWA can be glanded into a weatherproof enclosure with an earthing nut and lead to the CPCs.
 
Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it
Well I was thinking twin and earth (e.g. 6mm) would be cheaper and easier to run under floor boards etc.

Tbf I could use that blank space for a 40A MCB to supply the garage couldn't I 👀
 
The right hand side of your board with the lighting MCBs isn't RCD protected and the blank will be a spare way- so subject to a decent Ze you could simply fit an additional matching MCB for the new SWA, but it will have to be glanded properly, possibly into a small metal enclosure to ensure the armour is earthed. EDIT= Ah I've just seen your post stating T&E for the first part of the run, so the SWA can be glanded into a weatherproof enclosure with an earthing nut and lead to the CPCs.
So I could join the SWA into a IP65 rated box and attach a banjo, nut and cpc to Earth the SWA?
 
Cheers for the replies, much appreciated.

So the db is in the porch on the ground floor (highlighted red) and the first floor pic with red lines is my proposed route going under the floor boards or up into the loft.
You don't want to put the garage on the RCD side, just asking for trouble for the rest of the house being tripped by garage trouble.

If it can go on the MCB side (assuming SWA all the way, end of cable Zs acceptable, etc) then do that.

Off hand I don't know if RCBO are available for that board should you need 30mA additional protection there, but keeping it off the existing RCD would be sensible.

However, you might want to plan to replace that CU in the near future anyway so keep enough cable slack to along that.
 
Last edited:
You don't want to put the garage on the RCD side, just asking for trouble for the rest of the house being tripped by garage trouble.

If it can go on the MCB side (assuming SWA all the way, end of cable Zs acceptable, etc) then do that.

Off hand I don't know if RCBO are available for that board should you need 30mA additional protection there, but keeping it off the existing RCD would be sensible.

However, you might want to plan to replace that CU in the near future anyway so keep enough cable slack to along that.
You mentioned SWA all the way, is this because a join in cable with (T&E) would affect Zs readings or something?

Tbf I am leaning towards a board change at this point I won't lie.
 
Think about requirements for rcd protection of cables.
apart from the fact that where possible it is better to design a circuit with fewer or no joints in it.
 
ou mentioned SWA all the way, is this because a join in cable with (T&E) would affect Zs readings or something?
The point is that depending on the run, T&E might need RCD protection for Impact Protection. SWA definitely wouldn't for that reason. That is one reason why a few people are suggesting SWA all the way.

For fault protection purposes we need to be sure that a fault will trip the protective device (breaker) in the house. Until you know the Ze, the cable length and the cable size, the resistance (R1+R2) of the circuit can't be calculated and added to the Ze and then checked against the max Zs value for the device. (An RCD may be required for fault protection if the Zs exceeds the limit for the device. )

A further consideration is whether there are any metal services like water pipe for a tap entering the garage, as if anything needs bonding the far end you need to make sure the CPC is big enough to support this.

So this job can be easy (Low Ze, nothing to bond the far end) or quite difficult (High Ze, RCD needed for fault protection, larger SWA needed to bond services the far end, then decisions about selectivity of RCDs etc. etc.).
 
You mentioned SWA all the way, is this because a join in cable with (T&E) would affect Zs readings or something?

Tbf I am leaning towards a board change at this point I won't lie.
No joints and the t+e may need rcd protection depending on the route. Swa back to the board it a better solution and will cost minimally more due to the short length of the cable
 

Reply to Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top