Was called to a job yesterday where a company had completed an EICR on a house fed via a plastic water main with internal plumbing done completely in copper. They had put a c2 observation code for a lack of main protective bonding to the water. The customer had shown me the EIC cert she had been given by the original company who had completed a rewire on her property.
Disconnecting the earthing conductor at the intake position and completing an IR test to the internal stopcock on the water gave me a reading of 0 megohms. To me this has indicated that somewhere within this installation the copper pipework is earthy and deemed extraneous and does warrant a main bond. I did think this could be gaining a reading through the boiler gas connection (which is bonded) I am leaning on the side of advising the client to get the original contractor back to sort this. Opinions on this before doing so would be appreciated.
Disconnecting the earthing conductor at the intake position and completing an IR test to the internal stopcock on the water gave me a reading of 0 megohms. To me this has indicated that somewhere within this installation the copper pipework is earthy and deemed extraneous and does warrant a main bond. I did think this could be gaining a reading through the boiler gas connection (which is bonded) I am leaning on the side of advising the client to get the original contractor back to sort this. Opinions on this before doing so would be appreciated.