I've just had a potentially nasty issue involving a Burnt out, type 2 SPD. My customer has been using a small plasma cutter,
I don't have the exact details of the unit to hand, but it does plug in to a standard 13a socket outlet This is a new 100a single phase TT supply to a small commercial unit.
This was a very close call. The SPD, located directly next to the consumer mainswitch, had burnt out to such a degree, that it has (fortunately) taken out the fuse at the intake.
Is it possible, this cutter could produce enough transient voltage to create this issue?
I was led to believe, these devices should go open circuit when they fail.
 
I’m guessing that in that type of single mod SPD that they dont have the soldered joint that melts if any real current for a period is drawn via the now shorted Mov.
You could put the garage on its own supply which is how it should have been done in the first place.
My mention of the garage was just a scenario. This install only has 1 board. I suspect you might be right about the soldered connection, but to my mind, that doesn't make it right.
 
My mention of the garage was just a scenario. This install only has 1 board. I suspect you might be right about the soldered connection, but to my mind, that doesn't make it right.
I suppose analysing the waveform when the plasma cutter is being used is the way forward.
If it's actually bad enough to cause damage to other equipment, then throw it in the bin.
 
Are you sure their hasn't been a power surge from a local lightning strike, the plasma cutter may not be anything to do with it, such equipment should by design have its own suppression and smoothing circuitry to eliminate any unnacceptable interference on the power supply.
 
Are you sure their hasn't been a power surge from a local lightning strike, the plasma cutter may not be anything to do with it, such equipment should by design have its own suppression and smoothing circuitry to eliminate any unnacceptable interference on the power supply.
That's what I was thinking. It's not like this cutter was running for any great length of time either. Definitely no lightning strikes in the area though.
 

Reply to Plazma cutter causing SPD failure?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top