Even with an RCD rated at 100mA it could be cumulative leakage from multiple circuits.
 
44allan not a problem, i dont do loads and loads of commercial, do alot of domestic but time served, obviously with more domestic is 30ma, so any ideas on proving this and altering this? many thanks

Well............0.01 means it's a 100mA RCD..............does that help?
 
Just Thinking dont you think that 0.01 is very sensitive for a industrial unit using plenty of machines that could all be contributing to leaking to earth could this new machine bit tiping it over? etc

Leakage Clamp it mate then take it from there:)

I have compressor/welding sets the lot with 30mA 'cover'.
Don't need it, according to many,but it ain't tripping/it's tested regularly and it's far safer than just ADS .....IMO :)
If it trips............I'll assess then maybe put 100mA on the circuit as 'additional/supplementary' to the ADS.

If it's there and available use it:)
 
Does it mean 100mA?
Check your sums 44ALAN? ;)
Does the compressor have a VSD?

0.01 on an rcd means 100mA unless you can state otherwise VSD or not :)
Smiley face back at you and I raise :)

Big edit..............he meant 0.1 obviously :blush5:

And another edit..........bloody decimals fgs
 
Last edited by a moderator:
Was it sold as “working” if yes. The simple answer:
Supply the compressor via a none RCD protected supply. If this means a separate 3Φ sub-board off the incoming then so be it.
If sold as untested, buyer beware!

I really can’t understand anyone putting a compressor or any (none portable) machine on a RCD supply. It’s just asking for trouble.
 
You have covered the simple things already like the emergency stop and brake wiring systems? Could be something mechanical causing the trip rather than earth leakage (non fault).
Going by what you are saying the compressor doesn't trip on start up, is there a way to apply the brake via the control panel?
 
Last edited by a moderator:
If i was going to have an RCD on the supply to this compressor, it wouldn't be anything lower than 300mA. But then i wouldn't be installing an RCD in the first place, if it was my job!! lol!!

If this unit is tripping out the RCD main breaker, then it has to be a leakage problem doesn't it, otherwise it would be taking out the polly-phase MCB that's supplying the unit!! Is it that difficult within this factory unit installation, to provide a means of a separate supply to this compressor??
 

Reply to Please Help, Bloody Hydravane Compessor??? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top