44allan not a problem, i dont do loads and loads of commercial, do alot of domestic but time served, obviously with more domestic is 30ma, so any ideas on proving this and altering this? many thanks

Well............0.01 means it's a 100mA RCD..............does that help?
 
Just Thinking dont you think that 0.01 is very sensitive for a industrial unit using plenty of machines that could all be contributing to leaking to earth could this new machine bit tiping it over? etc

Leakage Clamp it mate then take it from there:)

I have compressor/welding sets the lot with 30mA 'cover'.
Don't need it, according to many,but it ain't tripping/it's tested regularly and it's far safer than just ADS .....IMO :)
If it trips............I'll assess then maybe put 100mA on the circuit as 'additional/supplementary' to the ADS.

If it's there and available use it:)
 
Does it mean 100mA?
Check your sums 44ALAN? ;)
Does the compressor have a VSD?

0.01 on an rcd means 100mA unless you can state otherwise VSD or not :)
Smiley face back at you and I raise :)

Big edit..............he meant 0.1 obviously :blush5:

And another edit..........bloody decimals fgs
 
Last edited by a moderator:
Was it sold as “working” if yes. The simple answer:
Supply the compressor via a none RCD protected supply. If this means a separate 3Φ sub-board off the incoming then so be it.
If sold as untested, buyer beware!

I really can’t understand anyone putting a compressor or any (none portable) machine on a RCD supply. It’s just asking for trouble.
 
You have covered the simple things already like the emergency stop and brake wiring systems? Could be something mechanical causing the trip rather than earth leakage (non fault).
Going by what you are saying the compressor doesn't trip on start up, is there a way to apply the brake via the control panel?
 
Last edited by a moderator:
If i was going to have an RCD on the supply to this compressor, it wouldn't be anything lower than 300mA. But then i wouldn't be installing an RCD in the first place, if it was my job!! lol!!

If this unit is tripping out the RCD main breaker, then it has to be a leakage problem doesn't it, otherwise it would be taking out the polly-phase MCB that's supplying the unit!! Is it that difficult within this factory unit installation, to provide a means of a separate supply to this compressor??
 

Reply to the thread, titled "Please Help, Bloody Hydravane Compessor???" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top