Carried out test on a socket circuit today and found open circuit on cpc’s and lives. Sorted out lives, but earths are driving me crazy. I’ve done all the obvious like connected one earth and then testing sockets etc etc.
In the end after disconnecting everything from earth bar( including main earth, all bonds and all cpc’s ) I was still getting a loop reading at all sockets. Max Zs reading taken was 1.26 ohms).
I can’t for the life of me find out where the sockets are getting a near perfect earth from.
Any info or ideas would be greatly appreciated.
 
Leave one of the cpcs connected to the earth bar and retest ring continuity to the disconnected one, if you have continuity you have a parallel path. I assume IR tests are clear.
 
Connect one cpc to its live at the board, test for continuity at each socket. Check in the last socket that gives continuity (if unclear how it is wired, check those that have highest continuity reading). If necessary, repeat with the other leg at the board. If no loose connections, it may be faulty between the 2 sockets identified.
Don't worry about the mysteriously good Zs with no cpc connected. It's not as important as the non-continuous cpc.
 

Reply to Please help my head is fried from open earths in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
714
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
522
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top