please help with this question

hi guys,

i need some help with an assignment and id appreciate it so so much if anyone can help me.

A circut which is supplied from DB 3 is protected by a 16A type C circut breaker and has a measured earth fault loop impednace of 1.35 ohms. Please determine (with reasons were applicable)

a. if this value of earth fault loop impendance is acceptable
b. at least one method of achieving disconnection should the device provide unacceptable in (a.) above with out re-wiring the circut.
c. at least one method of confirming the integrity of the live conductors of that circut under short circut conditions.

thanks alot guys for any help
 
That what threw me Ritch yes to confirm the cables integrity you carry out an IR .................but where does the short circuit come in, all I can think of was either

A) they are thinking about ADS to limit the time of the fault and therefore stress on the cable

B) Doing an IR test, after a fault occurred to check the cable
 
Upvote 0
As plugandsparks says for the value in the regs books this is at 70oC and you need to correct as Malcolm has said in post 3 a for the temperature at which the EFLI has been measured.....

Richard, you risk here putting the OP on the wrong track. The 70oC is likely to be the maximum operating temperature of the cable, though the specific type of cable has not been specified. It might be 90oC cable for all we know! The point is that the note on Table 41.3 states the values given are for when the conductors are at their normal operating temperature which is very much unlikely to be 70oC. The reference to Appendix 14 then points the reader to the 0.8 'rule of thumb' correction factor. This is of course a compromise, because there are so many unknowns, the actual conductor temperature at the time of the test and the actual conductor temperature under normal conditions being just two of those unknowns. Hence the expression 'rule of thumb'.
 
Upvote 0
Richard, you risk here putting the OP on the wrong track. The 70oC is likely to be the maximum operating temperature of the cable, though the specific type of cable has not been specified. It might be 90oC cable for all we know! The point is that the note on Table 41.3 states the values given are for when the conductors are at their normal operating temperature which is very much unlikely to be 70oC. The reference to Appendix 14 then points the reader to the 0.8 'rule of thumb' correction factor. This is of course a compromise, because there are so many unknowns, the actual conductor temperature at the time of the test and the actual conductor temperature under normal conditions being just two of those unknowns. Hence the expression 'rule of thumb'.


arrrr - the cat is out of the bag :-)
 
Upvote 0
A - meets maximum zs but exceeds rule of thumb, you probably should mention that
B - use a 16a btype breaker or 16a rcbo of via rcd protected way
c - very poor question, integrity of conductors ?? Test continuity and insulation resistance ? Calculate fault current and ensure your protective device will operate using regs ? (city & guilds question !!)
 
Upvote 0
I'm doing the same course and on the drawing it's stated that DB 3 is security system. Isn't it considered low voltage system and if so we have to check table 41.6 for Zs. But then I don't know how to answer b) and c).
 
Upvote 0

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top