hi, i went to a neighbours farm to help replace a broken motor, no problem. its supllied from a 3 phase board. however, the board is supllied via a 4 core armour with the armour providing the earth. i spoke to a colleague who says this is wrong. he says the submain should be rcd protected (300mA time delayed) banjoyed at the supply end, but not at the 2nd. board as this should have a tt stake fitted providing the earth. also the armour at the 2nd board should be insulated from the 2nd board so as to not export pme. is this correct
thanks
 
you check with the supplier, some will not let you earth remote buildings to their MET,s, so yes you may have to TT it however any metalic cable covering must be earthed earthing it to the TT system is the correct way at both ends if possible. any TT system must have a minimum 300ma rcd for fire protection.
 
hi

pme is not permitted in an agriculture installation, there fore the earthing arrangement needs to be tt.
so yes you could isolate pme at 3phase board and have 300ma rcd as main incomer then have 30ma rcbos for socket outlets, or make whole installation tt and have 300ma at origin.

hope this helps
 

Reply to please help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
508
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
979
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
909

Similar threads

  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
2K
T
  • Article
TTA Supports Lighthouse Charity and Appoints Mental Health Ambassador - From TTA TTA Supports Lighthouse Charity and Appoints Mental Health...
Replies
0
Views
188
The Tile Association
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top