Been asked to take a supply out to the gates (60m run) Not sure of the loading of gates but presume there not much.
Will be fitting a 16A breaker for the gates heres my calcs (tried 2.5mm but to my calcs there's to much volt drop heres my calcs for 4mm could someone just verify for me)
4mm 2core SWA = 11mV/A/m
11*60*16/1000=10.56V
230/5% = 11.5%
Therefore acceptable?
Thanksss!