Hello
Hope everyone if well with this cover-19 stuff going on
Quick question
I would like to put a power supply to a metal framed car port, the metal frame is buried into the ground so definitely introduces earth potential, the ground inside the carport is tarmac laid on top of soil
The power supply is coming from P.M.E house, I think the best option is to make the carport TT and install RCD protection, However I cannot achieve sufficient separation between PME bonded gas pipe and water pipes in the ground and the new earth electrode.
If I export the PME earth and bonding the metal structure then surely this is creating a large shock risk to anyone standing on the wet grass next to the car port and in contact with the metal structure if there was a PEN conductor fault.
Looking at 18th Edition Amendment 1 section on EV charging
722.411.4.1
(iv) Protection against electric shock in a single-phase installation is provided by a device which electrically disconnects the vehicle from the live conductors of supply and from the protective earth in accordance with Regulation 543.3.3.101(ii) within 5 s in the event of the utilisation voltage at the charging point, between the line and neutral conductors being grater than 253 C rms or less than 207 V rms. The device shall provide isolation and be selected in accordance with Table 537.4. Equivalent means of functionality could be included within the charging equipment. Closing or resetting of the device shall be possible only if the voltage between line and neutral conductors is in the range 207 to 253 V rms.
Maybe I could use a device like this but not for EV charging but instead to protect car port from open PEN
Although I cannot find anywhere to buy such a device
Many thanks
Marcus
Hope everyone if well with this cover-19 stuff going on
Quick question
I would like to put a power supply to a metal framed car port, the metal frame is buried into the ground so definitely introduces earth potential, the ground inside the carport is tarmac laid on top of soil
The power supply is coming from P.M.E house, I think the best option is to make the carport TT and install RCD protection, However I cannot achieve sufficient separation between PME bonded gas pipe and water pipes in the ground and the new earth electrode.
If I export the PME earth and bonding the metal structure then surely this is creating a large shock risk to anyone standing on the wet grass next to the car port and in contact with the metal structure if there was a PEN conductor fault.
Looking at 18th Edition Amendment 1 section on EV charging
722.411.4.1
(iv) Protection against electric shock in a single-phase installation is provided by a device which electrically disconnects the vehicle from the live conductors of supply and from the protective earth in accordance with Regulation 543.3.3.101(ii) within 5 s in the event of the utilisation voltage at the charging point, between the line and neutral conductors being grater than 253 C rms or less than 207 V rms. The device shall provide isolation and be selected in accordance with Table 537.4. Equivalent means of functionality could be included within the charging equipment. Closing or resetting of the device shall be possible only if the voltage between line and neutral conductors is in the range 207 to 253 V rms.
Maybe I could use a device like this but not for EV charging but instead to protect car port from open PEN
Although I cannot find anywhere to buy such a device
Many thanks
Marcus